Results 1 to 26 of 26
    May 2011
    India
    38
    106
    14
    Unhappy Calculating Reheat Capacity - For Humidity Control
    Hello,
    I am designing a HVAC system for an Equipment Room. Design set point is 22 deg C with 55% humidity. When I set the parameters and run in HAP, it says reheat is not required (@ setpoint of 55% RH).
    Now, there are instances when the internal sensible loads are not high enough to raise the supply air temperature (13 deg) to room setpoint, and I end up in a mess with very high RH in room, sometimes even condensation .
    I need to introduce a heater to control this. The issue is, the heater capacity is damn high if I consider the temperature difference of 9 (22 - 13), with the airflow of 12000l/s! Its more than the chiller capacity and its ridiculous!
    What would be the best solution to reduce this reheater capacity to an optimum level?
    N.B
    Im using Q=mCp(T2-T1) for calculating the capacity.
    Nevin.
    Re: Calculating Reheat Capacity - For Humidity Control
    12000 l/s seems a lot of airflow.
    How big is the room and what is the air change rate?
    May 2011
    India
    38
    106
    14
    Yes, its huge. Approx 530 sq.m, with internal heat dissipation of 90kW, unfortunately most of the time these electrical panels are in partial load, so no much heat dissipation from those! Approx 1ACH.
    So, with your 530 sq.m and an airflow of 12000l/s I calculate the height of your room to be 23 metres, is that correct?
    May 2011
    India
    38
    106
    14
    No, height is only 5m. That ACH I said was for fresh air replenishment, and not for supply air. Fresh air for the space is only 693l/s..
    See attached pics for input and output...
    5,667
    Have you thought of using a 3 port control valve on the chilled water circuit so that you can regulate cooling capacity to load?
    May 2011
    India
    38
    106
    14
    Hmm... that is a possibility. But, what would you suggest if the client insists on a reheat?
    As per the present control philosophy, humidity control overrides temperature control. Currently, even though the room temperature set point is reached, the RH is high. This calls for the valves to fully open supply to the AHU, and 'dehumidify' the air. Although dehumidification happens at the coil, I end up with a higher RH in the room!! So that 'philosophy' is not helping me. .
    5,667
    If most of your load is from electrical panels, where is your high humidity coming from?
    I was wondering that as well Frank.
    Surely the only source of moisture is from the fresh air intake so you only need reheat on the 693l/s to rematch the rooms 55%RH.
    Do you have a separate cooling/dehum coil in your fresh air makeup duct?
    May 2011
    India
    38
    106
    14
    Nope, I don't have a separate system to dehumidify the fresh air. I want re-orient you guys. This humidity is due to reduced internal loads. The OFF COIL air conditions, at 13deg C is with 95 - 90% RH. The internal sensible load is minimal, so the room RH is very high. This is my issue. It has nothing to do with fresh air. I am trying to increase this sensible load with a heater. :-(
    So the equipment is producing moisture is that correct?
    We are trying to establish where the moisture is coming from, is the room not air tight?
    5,667
    13c @ 95%RH????
    If you have a recirculating cooling system (air) with a small amount of fresh air make up, the humidity level should reduce with each pass of the evaporator, providing that your fresh air make up is not saturated and the evaporator is sized correctly.
    The electrical load in your room will not produce water vapour so where do you get 95% RH from?
    Physchrometric chart the condition change is almost a straight line so I'm confused.
    Oct 2008
    newbury
    1,444
    The offcoil humidity will be high due to the low off coil temperature. however it has relatively little water content so as soon as it mixes with the room air the room humidity will be low.
    to confirm we are still at the design stage here and not actual operating conditions?
    May 2011
    India
    38
    106
    14
    Yes, this is the point. The supplied air is almost at 95%RH, as it is with all air conditioning applications. But, the set point is reached, when this air absorbers the heat inside the room as represented as a straight line (between off coil and room conditions). The issue is, I don't have enough loads, for this conditioned air to absorb heat and this causes high Relative Humidity. The specific humidity is obviously low. . . Unfortunaly, its not in design stage, the system is operational. It gives me trouble during off peak period. Summers are good. I am worried about winters and rain, when the building envelop load is also less. . .
    See the attached psy chart. Don't bother the calculations, see the SHR, at part loads. scan_00032.jpg
    May 2011
    India
    38
    106
    14
    Yes, this straight line is under the assumptions that air picks up internal room loads, and achieves this set point. But what happens if there are no internal loads?
    Jul 2006
    865
    I am not an HVAC guy, so consider this a question more than a comment.
    If the conditioned space is at the required temp why cool the air going into it?
    Quote Originally Posted by NH3LVR View Post
    My next thought, control the space temperature better.
    As Frank suggested earlier use a three port valve on the cooling coil.
    Oct 2008
    newbury
    1,444
    Can you reduce the air volumes to match the load better.
    May 2011
    India
    38
    106
    14
    Good thought. The reason is again high RH. The space needs to be pressurized, hence I need some percentage of fresh air supply through out the year. This fresh air will causes varying RH (sometimes very high during winter and rain). To control these, and to meet the design RH set point of 50%, I need the chillers to be functional through out. . .
    May 2011
    India
    38
    106
    14
    No, unfortunately the AHUs and ducts are already in place. . I cannot change air flows... Heater is my only option.
    May 2011
    India
    38
    106
    14
    Thank you Brian, I am trying the same. Apparently, there are some issues with the controls. The client however insisted on a heater to be on a safer side... Its a panel room, and any downtime due to condensation is money lost.
  23. #23
    5,667
    So, from the data posted so far, I get that the room size is 530m2 x 5m high. Volume therefore is 2650m3.
    With a total air flow volume of 12000 l/s or 12 m3/s (16.30 ACH)
    Fresh air make up is 1 Air Change /Hour which equals to 2650m3/h or 0.736m3/s
    So,
    recirc air = (12 - 0.736) = 11.26m3/s
    fresh air = 0.736m3/s
    With the electrical VSD's producing very little, or any water vapour, we can assume that the excessive RH is coming from the fresh air make-up. If so, then it is only this element that needs treating and not the 12m3/s, either by shutting off the fresh air via humidity sensors when temp set point is reached or by dehum and re-heat.
    Either way, you will have to modify the existing duct system.
  24. #24
    May 2011
    India
    38
    106
    14
    So,
    Yes, I did the reheat option here.
  25. #25
    Oct 2008
    newbury
    1,444
    Quote Originally Posted by nevinjohn View Post
    a couple of VSD's will reduce energy consumption too?
  26. #26
    Sep 2003
    ISRAEL
    72
    4,248
    I would consider addin a smaller coil before the ac coil with evaporating temp of -8 c to freeze the water in the air with natural defrost every hour.