Re: Calculating Reheat Capacity - For Humidity Control
Hmm... that is a possibility. But, what would you suggest if the client insists on a reheat?
As per the present control philosophy, humidity control overrides temperature control. Currently, even though the room temperature set point is reached, the RH is high. This calls for the valves to fully open supply to the AHU, and 'dehumidify' the air. Although dehumidification happens at the coil, I end up with a higher RH in the room!! So that 'philosophy' is not helping me. .Last edited by nevinjohn; 26-03-2018 at 11:21 AM.