    Jan 2005
    Ireland
    38
    87
    Mitsubishi Mr Slim
    Hi guys
    I have a mitsubishi PUHZ-P125YHA with 2 high wall units.
    Compressor runs for 10 seconds and unit turns off no fault. Fans donít run. I have a hand held remote. I used the self diagnosis function which came up with 8 beeps . P8 , not sure if this is an old fault.
    Any thoughts
    70
    10,701
    52
    Re: Mitsubishi Mr Slim
    It could be P8 or U8 depending on the beeps, have you checked the outdoor unit errors?
    Service manual here.... http://bit.ly/2Htkewr
    Jan 2005
    Ireland
    38
    87
    Thanks Brian,
    The problem was I’d been work for 12 hours, it was dark and I was hungry , Faulty fan motor is the end result .
    70
    10,701
    52
    Well done buddy, that's the U8 then.
    64
    4,609
    I don't know many who cannot relate to that scenario.
    Well done.
    Jan 2005
    Ireland
    38
    87
    Cheers guys , thanks for the help