    Blowing VS sucking type fans



    Dear Friends,

    As you know most evaporator and condenser fans are sucking type fan instead blowing type fan.
    I now these rules :
    1 – In some cases Fan of condensers sucks air and throws it on semi-hermetic compressor and maybe help to cool these compressors better (Most of compressors such as hermetic and scroll types are suction cool and they be cool just by suction return and no need to cool by condenser fan)

    2 – Fan and evaporator coil should have counter-current flow to reach to maximum heat transfer (We can change structure of coil, Put suction collector near to inlet air of blowing fan then twice this type of evaporator would be counter-current)

    If we put these two above topics away, Why most (or always) fan of condensers/evaporators are sucking type instead blowing type ?

    Sincerely yours.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    75
    Posts
    11,192
    Rep Power
    60

    Re: Blowing VS sucking type fans

    The reason you want to use draw-thru air flow is due to the uniform flow pattern this creates over a coil. A blow-thru design has areas of the coil where higher air velocity occurs directly in front of the fan. On those adjacent areas farther away from the fan discharge the air velocity will tend to be much lower.

    The different air flow patterns through the coil affect the heat transfer and eventually the capacity is degraded.

    Mind you, there is a manufacturer who created a blast freezer that reduced cooling times by reversing the airflow so that each end of the cooling chamber received the coldest air at alternative times.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    138
    Rep Power
    21

    Re: Blowing VS sucking type fans

    Induced-draft design provides more even distribution of air across the bundle, since air velocity approaching the bundle is relatively low.
    This design is better suited for exchangers designed for a close approach of product outlet temperature to ambient-air temperature.
    Induced-draft units are less likely to recirculate the hot exhaust air.

  4. #4
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Blowing VS sucking type fans

    Sucking air over the condensor is the only way even as you say some compressors are suction cooled moving the air around a compressor does no harm only benefits it's operation.

  5. #5
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Blowing VS sucking type fans

    .

    At a more basic level it also helps with maintenance.
    Trying to clean a condenser or evaporator on the inside
    of the housing is a nightmare so having the dirt, dust and
    Debris on the outside is a lot easier to clean.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  6. #6
    Join Date
    Mar 2016
    Location
    IRAN
    Posts
    182
    Rep Power
    9

    Re: Blowing VS sucking type fans

    Thanks guys for your clear replies

  7. #7
    Join Date
    Mar 2008
    Location
    England
    Posts
    235
    Rep Power
    20

    Re: Blowing VS sucking type fans

    Do a little test for your self, place a smoke generator on the suction side of a fan and observe the ait flow in and out, you will see the turbulent nature of the air on the discharge side.