    Is there a 502 replacment drop in?



    Hi all,
    I have an old Hobart reach in freezer that just isn't getting down in temp like it used to. Nothing is iced up, all coils clean, fans,and compressor running. Guages say its running at about 5psi suction. I think it is slightly low on charge. Nameplate says 502 , I don't have any. I was wondering if I evac the system find the leak and repair it, what refrigerant could I put into this freezer without having to change the oil and filter driers? Thanks for help-refermadness



  2. #2
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Is there a 502 replacment drop in?

    Yes, 404a, you will use about 10% less refrigerant in the system

  3. #3
    Join Date
    May 2006
    Location
    Porto - Gaia
    Age
    47
    Posts
    10
    Rep Power
    0

    Re: Is there a 502 replacment drop in?

    Quote Originally Posted by wambat
    Yes, 404a, you will use about 10% less refrigerant in the system
    404a needs POE oil

    if you can replace some of the oil with AB oil you could use r402a

    think would be the best solution

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Is there a 502 replacment drop in?

    Why not simply add a drop-in like R408a?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Jan 2006
    Location
    TRACY CALIFORNIA
    Posts
    5
    Rep Power
    0

    Re: Is there a 502 replacment drop in?

    Thanks for replies. So which refrigerant should I use? Everyone had a different answer. A drop in replacement is preferred. Thanks again

  6. #6
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Is there a 502 replacment drop in?

    Peter has the right answer.

    Use 408A.

    Then you dont have to change the oil.I have done it many times.

  7. #7
    Join Date
    Apr 2006
    Location
    UK
    Posts
    77
    Rep Power
    19

    Re: Is there a 502 replacment drop in?

    Isceon 69l drop in.

  8. #8
    Join Date
    Mar 2006
    Location
    West London
    Posts
    12
    Rep Power
    0

    Re: Is there a 502 replacment drop in?

    Hi,
    Drop in for R502.
    R408A
    R402A
    R402B
    R403B
    HP80
    HP81
    69L
    Dont forget to change the drier,
    Hope this helps,
    Cheers,
    Raven

  9. #9
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Is there a 502 replacment drop in?

    I invite to go here and notice the lubricant recommended. As you are in California this should be easy to obtain It's called R422 or MP79
    http://refrigerants.dupont.com/Suva/.../isceon79.html

    Benefits


    provides easy, quick, cost-effective retrofits—easier retrofit than R-404A and R-507
    non-ozone-depleting HFC
    in most cases no change of lubricant type during retrofit is required -- compatible with traditional and new lubricants
    enables continued use of existing equipment
    20% lower Global Warming Potential (GWP) vs. R-404A and R-507
    can be topped off during service without removing the entire refrigerant charge
    Last edited by wambat; 07-06-2006 at 11:59 PM.

  10. #10
    Join Date
    Jan 2006
    Location
    TRACY CALIFORNIA
    Posts
    5
    Rep Power
    0

    Re: Is there a 502 replacment drop in?

    Hey thanks for the feedback I think I will go with the
    408A as I have a jug of it on site. I have a ton of different refrigeration equipment in my building that I am responsible for maintaining so I am sure you will be hearing from me again. Thanks again refermadness

  11. #11
    Join Date
    Jan 2006
    Location
    Adelaide , Australia
    Posts
    192
    Rep Power
    19

    Re: Is there a 502 replacment drop in?

    Yay the R408 won in the end , you can put it on top of the remaining R502 as well you know , it saves trying to do something with the "reclaimed " gas afterwards .

  12. #12
    Join Date
    Jan 2006
    Location
    Adelaide , Australia
    Posts
    192
    Rep Power
    19

    Talking Re: Is there a 502 replacment drop in?

    Quote Originally Posted by refermadness
    Hey thanks for the feedback I think I will go with the
    408A as I have a jug of it on site. I have a ton of different refrigeration equipment in my building that I am responsible for maintaining so I am sure you will be hearing from me again. Thanks again refermadness
    Quote Originally Posted by rdocwra

    Why do we have all these new gases available especially when you consider a lot of them contain much the same (R134 in R404)
    Could it not be possible to the manufactures to standardise gases or is it just a ploy to have lots of them & keep the price up
    Regards
    Raymond
    When ozone depleting rules kicked in about all it did was give those clever marketing people an opportunity to market yet another product . In Australia there's MANY MANY gases avaliable most of them do the same job , and are probably the same gas underneath . We just make all new jobs R404 . Retro refits are just with the drop in gases R409 & R408

  13. #13
    Join Date
    Jul 2006
    Location
    England
    Age
    57
    Posts
    18
    Rep Power
    0

    Re: Is there a 502 replacment drop in?

    Definately R408a, it is very happy with mineral oil, however I would not mix it with R502!!!!!!

    BTW, Whats the point of using a drop in refrigerant if you have to change to AB oil, it's not really a drop in then is it?

  14. #14
    Join Date
    Jun 2005
    Location
    U.K.
    Posts
    16
    Rep Power
    0

    Re: Is there a 502 replacment drop in?

    hi
    the best is use 408a if you have a site glass just charge it till it is clear

  15. #15
    tommy 1234's Avatar
    tommy 1234 Guest

    Re: Is there a 502 replacment drop in?

    i have a freezer that takes r-408 but i have alot of r-502 can i mix the two together???

  16. #16
    tommy 1234's Avatar
    tommy 1234 Guest

    Re: Is there a 502 replacment drop in?

    what will happen if r-502 and r-408 are mixed together there is only a ten degree difference in the refrigerants

  17. #17
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Is there a 502 replacment drop in?

    r408a is a drop-in, the name says itself. , sure you can.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  18. #18
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Is there a 502 replacment drop in?

    I have always used R408, just fling it in on any R502 job on top of the remaining gas and oil.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  19. #19
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Is there a 502 replacment drop in?

    R408A, as the others have noted.
    Last edited by powell; 09-06-2008 at 02:07 PM.

  20. #20
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: Is there a 502 replacment drop in?

    i use 408 but call it 69 is it the same thing???

  21. #21
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Is there a 502 replacment drop in?

    Quote Originally Posted by thebigcheese View Post
    i use 408 but call it 69 is it the same thing???
    Isceon 69 is R403b.

  22. #22
    Join Date
    Jun 2001
    Location
    Gloucestershire
    Posts
    13
    Rep Power
    0

    Re: Is there a 502 replacment drop in?

    Quote Originally Posted by Raven View Post
    Hi,
    Drop in for R502.
    R408A
    R402A
    R402B
    R403B
    HP80
    HP81
    69L
    Dont forget to change the drier,
    Hope this helps,
    Cheers,
    Raven
    In 18 months time you won't be able to use virgin product of any of the above in Europe, however the DuPont ISCEON MO79 replaces all of them.

  23. #23
    Join Date
    Oct 2007
    Location
    NZ
    Posts
    85
    Rep Power
    17

    Re: Is there a 502 replacment drop in?

    Quote Originally Posted by Andy T View Post
    Isceon 69l drop in.
    Have to agree , ive used lots of 69L in everything from blast freezers to small display cabinets with no oil change

  24. #24
    Join Date
    Jul 2008
    Location
    Singapore
    Posts
    11
    Rep Power
    0

    Re: Is there a 502 replacment drop in?

    Hi!,

    Best drop-in solution to replace R502 is DuPont Isceon 79. Most cases no oil change required.

    Regards
    Koh/Singapore

  25. #25
    al595017's Avatar
    al595017 Guest

    Re: Is there a 502 replacment drop in?

    Hi, Can drop ins be used the other way round? ie can R408a be used to charge a R404a sytem if no 404a is readily available? What would be the effect on system?

    Thanks

  26. #26
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Is there a 502 replacment drop in?

    the new refigerants react with the old oils,r22 is an example as works with poe & mineral oils
    mmm to beer or not to beer...........lets drink breakfast

  27. #27
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: Is there a 502 replacment drop in?

    Quote Originally Posted by refermadness View Post
    thanks for replies. So which refrigerant should i use? Everyone had a different answer. A drop in replacement is preferred. Thanks again
    69l works ok for me

  28. #28
    al595017's Avatar
    al595017 Guest

    Re: Is there a 502 replacment drop in?

    Quote Originally Posted by koh View Post
    Hi!,

    Best drop-in solution to replace R502 is DuPont Isceon 79. Most cases no oil change required.

    Regards
    Koh/Singapore
    Any advice available?
    According to the makers Isceon 79 is better than R404a in some applications so would I be right in thinking that it could replace R404a? If so would it be a 5% less charge as suggested for retrofitting R502, R408a etc or the same charge as R404a?

    Thanks

    A

  29. #29
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Is there a 502 replacment drop in?

    408 for me works fantastic on medium temp too.go the croweaters
    mmm to beer or not to beer...........lets drink breakfast

  30. #30
    davids2212's Avatar
    davids2212 Guest

    Re: Is there a 502 replacment drop in?

    hi
    i had a job today with a foster freezer! it had no refridgerant in it but needed r502. i repaired the cabinet and then filled with r408a but the temp went from +22C and fell and sat around -1C !!!! have i got a control problem? HELP please!!

  31. #31
    Join Date
    Jun 2005
    Location
    U.K.
    Posts
    16
    Rep Power
    0

    Question Re: Is there a 502 replacment drop in?

    need to know more about the cabinet is it control by expansion valves or capalary
    Hi be happy

  32. #32
    Join Date
    Apr 2006
    Location
    UK
    Posts
    77
    Rep Power
    19

    Re: Is there a 502 replacment drop in?

    What Are the gauge pressures.You probably only got Suction connected.Chances are you have a low suction pressure.
    Reasons:
    Weight of charge incorrect
    Moisture in system.Is the suction going into a vac and then shooting back up Again.
    Blocked dryer. or capalary
    Are the fans running.The tempurature won't drop until the Evap is cold enough to start the fans.
    It could be lots of other things but we need more info from you.
    I use R69L for a replacement for R502
    Worked perfect in everything I used It In.

  33. #33
    davids2212's Avatar
    davids2212 Guest

    Re: Is there a 502 replacment drop in?

    I have only been doing this for three months so any help is much appreciated (passing C+G 2079 doesn’t make you a fridge engineer!!!) Got to play with the freezer for a couple of hours today! From previous engineer documentation back from 1993 they filled the freezer with 450g of r502. I put in 300g of r408a today and the freezer sat a –11deg C. low pressure reading 1.8 bar and frost build up on low pressure (suction) side before compressor (have I still over filled it?). The defrost heaters are not stuck on, good air flow, fans working and new door seals. Ladies in the canteen told me that the freezer always had a problem reaching temp and from when I first got the job there was a lot of ice build up on the evaporator.

    it uses capalary and i do only have the suction line connected but it doesnt go into a vac and shoot back up it stays quite still at 1.8 bar!

    will R502 still work or do i need to get R69L


    Please somebody put me out of this misery, what have I missed!

  34. #34
    Join Date
    Apr 2006
    Location
    UK
    Posts
    77
    Rep Power
    19

    Re: Is there a 502 replacment drop in?

    Engineer log.Nice.Sounds to me that you need to find the data plate on the room.It should have the refrigerant and weight of charge.Also check the comp for a match to the old gas.I would trust that more than the Engineers log.I charge the same amount of 69L as on the plate.If you do that correct.Then you can rule out it's somthing you have done wronge.Also with frosting on the coil and the unit never before working well.You should be looking for faults for that too.These faults can be tricky to find.Your at -11. thats better than yesterday.
    I would charge it with another 150g.If it starts frosting back on the suction bad.Then I would double check the airflow.Fan rotation.Blocked air flow(boxes blocking intake,Panel put back wronge or missing)that sort of thing.
    If it has never worked right.Is it really a freezer box,or has someone decided to convert it. or just set the temp down.Being on R502 suggest it is.but look at the name plate.there are two ways to find a fault.
    No.1 First look for the fault.
    No.2 Check everything to see if it all working correct.and stumble on the fault.Starting with the most likely.
    You have only been doing it for 3 months.Call your boss and ask for onsite help on this one.
    Last edited by Andy T; 12-11-2009 at 09:31 AM.

Similar Threads

  1. A question about the pressure drop in coil .
    By jackcn in forum Fundamentals
    Replies: 20
    Last Post: 13-12-2008, 05:10 PM
  2. pressure drop of pump return line ammonia
    By Moeller in forum Fundamentals
    Replies: 5
    Last Post: 04-09-2007, 05:21 AM
  3. pressure drop of two phase flow in valves
    By Hansss in forum Fundamentals
    Replies: 2
    Last Post: 24-06-2006, 05:10 PM
  4. Replies: 17
    Last Post: 25-08-2003, 09:56 PM
  5. TEV capacity related to pressure drop
    By DaBit in forum CPU Overclockers
    Replies: 8
    Last Post: 06-12-2002, 05:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •