    Daikin FTX25K2V1B - Cancel auto restart



    Hi all,

    Anyone know how to cancel auto-restart function on this model? Went through the service manual but could not find anything.



  2. #2
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Daikin FTX25K2V1B - Cancel auto restart

    Assuming the field settings are the same across the range, the info I've got for older models is field setting 22-5-02 is factory setting, 22-5-01 to disable it. Might not be the way but the only info I've got, be worth a try.

    Cheers,
    Andy.

  3. #3
    Join Date
    Jun 2009
    Location
    Malta
    Age
    47
    Posts
    21
    Rep Power
    0

    Re: Daikin FTX25K2V1B - Cancel auto restart

    Thanks Andy. Can this be done with the infra-red remote or would I need a wired controller?

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin FTX25K2V1B - Cancel auto restart

    Looks like that model does not allow changing of that function.

    Is there a reason why you want to disable it?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Jun 2009
    Location
    Malta
    Age
    47
    Posts
    21
    Rep Power
    0

    Re: Daikin FTX25K2V1B - Cancel auto restart

    The unit is installed in a rented room. Its power supply is switched off whenever the door is opened. But if you leave the room and close the door, power is restored and it will start again.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin FTX25K2V1B - Cancel auto restart

    You could do the start/stop on the door opening by adding a krp board instead of dropping mains power.
    Every time you drop mains power you disable the crankcase heater function.

  7. #7
    Join Date
    Jun 2009
    Location
    Malta
    Age
    47
    Posts
    21
    Rep Power
    0

    Re: Daikin FTX25K2V1B - Cancel auto restart

    Thanks Frank, will get the krp board.