    R404a vs r22



    Dear Friends,

    First of all, Thanks for participating in my questions.

    Suppose that one compressor can work with R22 and R404A both of them.
    As we know in same situation (Same evaporator and condenser pressure and temp.) Cp of R404A is higher than R22 and we see on catalogues that Capacity of compressor with R404A is higher than R22.

    But at Maneurop (Danfoss) compressors I saw that capacity of compressor (in same evp. Temperature) at Tcondenser 30 & 40 with R404A is higher than R22 but at Tcondenser = 50C capacity of compressor with R22 is higher than R404A !

    Does it have any explanation ? Why at Tcondenser = 50C this time capacity of compressor with R22 is higher than R404A ??

    Sincerely yours.



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: R404a vs r22

    .

    I looked both up on a Ph chart and the only obvious difference if you plot both with a 10K superheat from the evaporator R404A is within 10K of it's critical temperature but R22 is more that 20K away from it's critical temp??

    404 is a blend also and as a blend it is only as good as it's component parts, R22 being a singular pure fluid would be more stable nearer it's critical point.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Mar 2016
    Location
    IRAN
    Posts
    182
    Rep Power
    9

    Re: R404a vs r22

    Quote Originally Posted by Rob White View Post
    .

    I looked both up on a Ph chart and the only obvious difference if you plot both with a 10K superheat from the evaporator R404A is within 10K of it's critical temperature but R22 is more that 20K away from it's critical temp??

    404 is a blend also and as a blend it is only as good as it's component parts, R22 being a singular pure fluid would be more stable nearer it's critical point.

    Rob

    .
    Thanks rob. Nice and clear reason.

  4. #4
    Join Date
    Mar 2016
    Location
    IRAN
    Posts
    182
    Rep Power
    9

    Re: R404a vs r22

    Quote Originally Posted by Rob White View Post
    .

    I looked both up on a Ph chart and the only obvious difference if you plot both with a 10K superheat from the evaporator R404A is within 10K of it's critical temperature but R22 is more that 20K away from it's critical temp??

    404 is a blend also and as a blend it is only as good as it's component parts, R22 being a singular pure fluid would be more stable nearer it's critical point.

    Rob

    .
    Thanks rob. Nice and clear reason.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •