Results 1 to 5 of 5
Thread: Daikin vrv REYQ8P-48P
-
25-02-2018, 01:05 PM #1
Daikin vrv REYQ8P-48P
I have a fault code come up on a display of E3 which says it could be
High Pressure
Defect of high pressure switch
Defect of outdoor unit main Pc board A1P
Instantaneous power failure
Faulty high pressure sensor
Where the best place to check first as all the zone areas are coming up faults also where I live the Daikin back up is terrible
Or does any one have info on these units this is 10 years old
-
25-02-2018, 03:06 PM #2
Re: Daikin vrv REYQ8P-48P
All of the indoor unit controllers are reporting the fault - E3 High pressure. As reported somewhere on the system.
First of all, check that the outdoor fans operate and that the coil is clean.
Download the Daikin App for your phone from the Google or Apple store (free) and follow the remedy for the E3 error
-
25-02-2018, 04:43 PM #3
Re: Daikin vrv REYQ8P-48P
Hi this is of one controller and you can control the system through a lap top
-
25-02-2018, 05:05 PM #4
Re: Daikin vrv REYQ8P-48P
I have a daikin service checker here in Tenerife if it gets that bad
http://www.daikintech.co.uk/Data/VRV...P(7)Y1B_SM.pdf
-
26-02-2018, 03:14 PM #5
Re: Daikin vrv REYQ8P-48P
This is the App https://play.google.com/store/apps/d...n.aircon&hl=en