    Which one is true ?



    Dear friends,
    I had discussion about this matter in a group yesterday. I have a question.

    Suppose we have a 1 ph hermetic compressor.

    1 - I was telling when suction pressure and discharge pressure are near to each other it means compression ratio is near to 1 and compressor will start better and easier (We have this matter at air-conditioning system compressor).

    2 - Others insist on this matter when suction pressure is low, For example when we pump down compressor before off cycle, Compressor will start easier because compressor has not high load on suction and cylinder while wants to start.

    I know while suction pressure decreases, Compressor load and working ampere would decreases, It is clear. But what about starting time ? In which case compressor would start easier ?

    Which one is true ?

    Sincerely yours.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Which one is true ?

    2 Is untrue.

    It is the difference between the suction and discharge pressures that affect the power required to start the motor.

    That is why we have LST Low Starting Torque and HST High Starting Torque compressors.

    This Danfoss document may help....

    https://www.google.co.uk/url?sa=t&so...MdjY7X_r4zZvF8
    Last edited by Brian_UK; 23-02-2018 at 08:31 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2016
    Location
    IRAN
    Posts
    182
    Rep Power
    9

    Talking Re: Which one is true ?

    Quote Originally Posted by Brian_UK View Post
    2 Is untrue.

    It is the difference between the suction and discharge pressures that affect the power required to start the motor.
    Dear Brian_UK,

    OK 2 True.

    1 - But I saw a compressor that works in this shape :
    There was a solenoid valve between discharge and suction pipe. Before start this solenoid valve opens route between suction and discharge pipe, Compressor starts and after few second this solenoid valve close this route. This solenoid valve for few second just wants to equalize these two pressures between suction and discharge.

    2 – Please find my photo at below, There are some lines that I mentioned with yellow color form SUPCO company catalogue.

    Sincerely yours.



    Sorry Brian_UK , I thought that you told me item 2 is true !!!! sorry

    1111.jpg
    Last edited by A.Mortezania; 23-02-2018 at 08:36 PM.

  4. #4
    Join Date
    Mar 2016
    Location
    IRAN
    Posts
    182
    Rep Power
    9

    Re: Which one is true ?

    Quote Originally Posted by Brian_UK View Post
    2 Is untrue.

    It is the difference between the suction and discharge pressures that affect the power required to start the motor.

    That is why we have LST Low Starting Torque and HST High Starting Torque compressors.

    This Danfoss document may help....

    https://www.google.co.uk/url?sa=t&so...MdjY7X_r4zZvF8
    Thanks a lot

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Which one is true ?

    I was referring to piston compressors.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Which one is true ?

    The old prestcold r bodies 5 hp and up had a valve if I am not mistaken man they ran like a sewing machine if treated right!

  7. #7
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Which one is true ?

    Mortezania
    You can get Txvs which have an internal bleed through the orifice to help the system pressures equalise quickly . The bleed rate is only a small percentage of the main orifice so that the superheat control still operates correctly

  8. #8
    Join Date
    Mar 2016
    Location
    IRAN
    Posts
    182
    Rep Power
    9

    Re: Which one is true ?

    Quote Originally Posted by Glenn Moore View Post
    Mortezania
    You can get Txvs which have an internal bleed through the orifice to help the system pressures equalise quickly . The bleed rate is only a small percentage of the main orifice so that the superheat control still operates correctly
    Dear Glenn Moore,

    Thanks for your advice. Do you have any documents or photo form this type of TXV ?

    Sincerely yours.

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Which one is true ?

    We have in the past pointed you towards libraries containing the information you seek.

    Please make use of these resources.

    http://sporlanonline.com/literature-...nal-materials/
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  10. #10
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Which one is true ?

    Hi, A.Mortezania

    Quote Originally Posted by A.Mortezania View Post
    Dear friends,
    I had discussion about this matter in a group yesterday. I have a question.

    Suppose we have a 1 ph hermetic compressor.

    1 - I was telling when suction pressure and discharge pressure are near to each other it means compression ratio is near to 1 and compressor will start better and easier (We have this matter at air-conditioning system compressor).

    2 - Others insist on this matter when suction pressure is low, For example when we pump down compressor before off cycle, Compressor will start easier because compressor has not high load on suction and cylinder while wants to start.

    I know while suction pressure decreases, Compressor load and working ampere would decreases, It is clear. But what about starting time ? In which case compressor would start easier ?

    Which one is true ?

    Sincerely yours.
    In your first post statement no. 1 is correct ... compressor is going to start easier ... when both pressures are equalized i.e. close each other .... valid for any type of compressor ....

    Second statement is wrong .... but pump down is another way to equalize suction and discharge pressure within compressor ... compressor can start easier because there is no high load on discharge as a consequence of low pressure on suction ... amperes of compressor depend only on discharge pressure ... i.e. mass of refrigerant to move ... in case of low suction pressure amount of work is smaller due to low mass of refrigerant to move from suction to discharge ...



    Quote Originally Posted by A.Mortezania View Post
    Dear Brian_UK,

    OK 2 True.

    1 - But I saw a compressor that works in this shape :
    There was a solenoid valve between discharge and suction pipe. Before start this solenoid valve opens route between suction and discharge pipe, Compressor starts and after few second this solenoid valve close this route. This solenoid valve for few second just wants to equalize these two pressures between suction and discharge.

    2 – Please find my photo at below, There are some lines that I mentioned with yellow color form SUPCO company catalogue.

    Sincerely yours.



    Sorry Brian_UK , I thought that you told me item 2 is true !!!! sorry

    1111.jpg


    In your second post statement 1 - with by-pass valve between discharge and suction can help for easier start .... this valve can be open for some short time ... 5-10 seconds max otherwise there is possibility to have too high suction super-heat and consequently high discharge temperature ... leading to alarm and shutdown ... this is generally installed on screws, because industrial piston compressors can be started almost unloaded what is not case with screws ... can be installed also on hermetic piston and scrolls ...

    Statement 2 is kind of "snake water" - this can be of some help, but in general coming into this position (hard start) must be solved during project design phase ... otherwise no help i.e. any solution will cost a lot and definitely not good ...


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  11. #11
    Join Date
    Mar 2016
    Location
    IRAN
    Posts
    182
    Rep Power
    9

    Re: Which one is true ?

    Quote Originally Posted by Josip View Post
    Hi, A.Mortezania



    In your first post statement no. 1 is correct ... compressor is going to start easier ... when both pressures are equalized i.e. close each other .... valid for any type of compressor ....

    Second statement is wrong .... but pump down is another way to equalize suction and discharge pressure within compressor ... compressor can start easier because there is no high load on discharge as a consequence of low pressure on suction ... amperes of compressor depend only on discharge pressure ... i.e. mass of refrigerant to move ... in case of low suction pressure amount of work is smaller due to low mass of refrigerant to move from suction to discharge ...







    In your second post statement 1 - with by-pass valve between discharge and suction can help for easier start .... this valve can be open for some short time ... 5-10 seconds max otherwise there is possibility to have too high suction super-heat and consequently high discharge temperature ... leading to alarm and shutdown ... this is generally installed on screws, because industrial piston compressors can be started almost unloaded what is not case with screws ... can be installed also on hermetic piston and scrolls ...

    Statement 2 is kind of "snake water" - this can be of some help, but in general coming into this position (hard start) must be solved during project design phase ... otherwise no help i.e. any solution will cost a lot and definitely not good ...


    Best regards, Josip