    small water chiller & diversity factor



    Chaps

    we're looking at swapping out an old 10kw water chiller . Client suggests it's been wrong since installed and was told it was 'way oversized'. Our investigations suggest it's sized for the fan coils but not the 16a fuse rating.!

    anyhoo there are 3 fan coils,

    bedroom 1= 2kw
    lounge =5kw
    second bed 3.5kw

    The chiller size would have been spec'ed by the architect or builder as a 100% matched load/demand .

    BUT we size ac over here for expected load and on such a multi 10kw DX use a 7kw outdoor (2 x bedrooms OR lounge running). Never have a problem.

    would the panel suggest or fit a downsize to 7kw chiller would be acceptable. Remember this isn't an office all on/off type environment so load differs according to time. Client said he never uses bed 2 in any case but I'm not counting on that . He doesn't rent so there isn't the usual holiday makers abuse happening either.

    we can only fit a new outdoor chiller as the building is impossible to retro a complete new multi so that's a non starter.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: small water chiller & diversity factor

    I've forgotten where you are based now but would an air to water heat pump be of any use or is there no need for winter heating?

    Sorry, in answer to your question I would go for the 7kW.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: small water chiller & diversity factor

    Chillers hardly run on full capacity.
    Capacity is based on certain in and out temp so when the water temp is higher then in and out temp, capacity rises and vise verse.
    A 7 KW will have no problem controlling the temp in the rooms.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: small water chiller & diversity factor

    Easy way to tell if the unit is oversized, but only if it is in working condition.

    Wait for a hot day (max load), run the unit, fan coils on full cooling, and then measure the water temp difference (flow and return). Q = m c (t1-t2). If you have less than 6K diff then the unit is over sized.

    With a 10kW chiller, I would assume around 0.39 l/s flow rate.

  5. #5
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    439
    Rep Power
    31

    Re: small water chiller & diversity factor

    I would retain the 10Kw chiller as this is then capable of doing the full duty required from end of June to October.
    Have a look at the piping flow & return, I would guess chiller problems were due to insufficient flow.
    Select your new chiller with integrated tank and pump, readily available in 10Kw size. This will then have some thermal buffer inbuilt.

    On your flow and return to chiller put in a bypass loop and use this to maintain chiller rated flow.
    I love the smell of Ammonia in the morning!

  6. #6
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,445
    Rep Power
    37

    Re: small water chiller & diversity factor

    Quote Originally Posted by Brian_UK View Post
    I've forgotten where you are based now but would an air to water heat pump be of any use or is there no need for winter heating?

    Sorry, in answer to your question I would go for the 7kW.
    Tenerife, Little need for heating although we have had an unusually cold winter

  7. #7
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,445
    Rep Power
    37

    Re: small water chiller & diversity factor

    Quote Originally Posted by hookster View Post
    I would retain the 10Kw chiller as this is then capable of doing the full duty required from end of June to October.
    Have a look at the piping flow & return, I would guess chiller problems were due to insufficient flow.
    Select your new chiller with integrated tank and pump, readily available in 10Kw size. This will then have some thermal buffer inbuilt.

    On your flow and return to chiller put in a bypass loop and use this to maintain chiller rated flow.

    as I say problems were fuse rating not chiller rating or flow.

  8. #8
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,445
    Rep Power
    37

    Re: small water chiller & diversity factor

    Quote Originally Posted by frank View Post
    Easy way to tell if the unit is oversized, but only if it is in working condition.

    Wait for a hot day (max load), run the unit, fan coils on full cooling, and then measure the water temp difference (flow and return). Q = m c (t1-t2). If you have less than 6K diff then the unit is over sized.

    With a 10kW chiller, I would assume around 0.39 l/s flow rate.
    non operating hence the need to change. :-)

  9. #9
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,445
    Rep Power
    37

    Re: small water chiller & diversity factor

    P_20180220_093458[1].jpgthis is the unit in question.