    R32 -Use of flares on indoor uniits



    We have just attended an R32 training course and posed the question in regard to indoor units and the use of flares inside the room.

    In some install manuals the manufacturers ask for the flares to be made outside of the room and in others, from the same manufacturer there is no such stipulation.

    We received a reply that there is no special requirement (legislation?) for the location of the flare connections, so the only reason would be for a product requirement.

    We will continue to cut the flares off on wall mounted fan coils and then braze, but on other fan coil types that is not so easy, so until we hear different we will use the flares on those with very short stubs outside the units.

    Comments?


    My tools. Screw driver, Hammer & a Condom:
    If you can't fix it, hit it. If you can't hit it, F**k it!

  2. #2
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14

    Re: R32 -Use of flares on indoor uniits

    I always braze the indoor connections!!

  3. #3
    Join Date
    Jun 2009
    Location
    Malta
    Age
    47
    Posts
    21
    Rep Power
    0

    Re: R32 -Use of flares on indoor uniits

    That's a question I asked Daikin re VRV indoor units. They said it would invalidate warranty.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: R32 -Use of flares on indoor uniits

    And what is the reasoning behind that decision off flare cutting?
    Properly made and properly tightened flare joint is as good as welded joint! I have proved that (at least to myself) in my 20 and more years of flaring joints for split air conditioners.
    Last edited by nike123; 18-02-2018 at 03:26 PM.

  5. #5
    Join Date
    Aug 2009
    Location
    england
    Age
    66
    Posts
    31
    Rep Power
    0

    Re: R32 -Use of flares on indoor uniits

    Over the years i have done hundreds of leak & pressure tests, the vast majority of these leaks are on the indoor flare nuts, either the nut has split or not tight enough due to the connection being difficult to make, i would always cut them out.

    Skilts

  6. #6
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    58
    Posts
    522
    Rep Power
    19

    Re: R32 -Use of flares on indoor uniits

    So many different opinions regarding flares, the opinion that is treat as a fact that a flare will eventually leak seems to be applied on a system with a care refrigerant. Manufacturers instructions and guidance seem to conflict with legislation these days.

    If a flare is done correctly and not rushed it shouldn't leak. I don't possess the care refrigerant ticket but I do possess the LPG ticket. So correct me if I'm wrong but without looking into the requirements, I would assume if the units charge volume is such that if it leaks into the room or compartment it is installed, it will be below the lower flammability limit. If the lower flammability limit cannot be kept within safe limits resulting from a leak, then lower ventilation should be installed?

    I know if you were connecting to units, branching off and joining within a hazardous area, you will only be allowed to to flare. As any hot works would not be permitted without stopping production and applying contingency methods, the risks and associated cost would dictate other methods of cooling or heating.
    Training may be finished but experience is never complete.

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: R32 -Use of flares on indoor uniits

    I've seen flares leak and I've seen brazed joints leak......

  8. #8
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    58
    Posts
    522
    Rep Power
    19

    Re: R32 -Use of flares on indoor uniits

    Indeed, along with thin walled coils and safety devices on receivers. But they are all CE benchmarked, so that must mean it's safe for it to leak!
    Training may be finished but experience is never complete.

  9. #9
    Join Date
    Dec 2010
    Location
    devon
    Age
    52
    Posts
    837
    Rep Power
    24

    Re: R32 -Use of flares on indoor uniits

    I still really don't understand why there is any flares on any units we always remove flares where possible I don't really no why new a.c. units don't come with Stubbs on condenser like most fridge condenser when braised you simply don't get as many leaks I realise that very few acs leak on flares but they occasionally do leak braise where you can simple

  10. #10
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    567
    Rep Power
    24

    Re: R32 -Use of flares on indoor uniits

    Hi Charlie
    I agree that welding the pipe is a better option but I think the reason they have flares is no Hot Work permit is required, installers don't have to have OFN or an Oxy, they only need a flaring tool. I think manufacturers want to make it as simple as possible so non-fridgies can install.
    Regards
    Paul
    Born to fish, forced to work

  11. #11
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,445
    Rep Power
    37

    Re: R32 -Use of flares on indoor uniits

    Did our first R32 install this week. A Mk II Emura. No different to the r410a and no training needed. In fact I'm not sure there is any training facility over here in Tenerife?. Anyhoo Pipe connections were through the wall

  12. #12
    Join Date
    May 2006
    Location
    Sussex
    Posts
    364
    Rep Power
    20

    Re: R32 -Use of flares on indoor uniits

    I think if you are installing R32 systems, it would be better to braze the indoor connections rather than flare them so as to improve the fire-safety risk, even with the blasé {not blaze} play-down by the Daikin trainers. Many engineers braze the inside joints anyway.

    BUT, all this fuss over R410a refrigerant is a bit strange. I keep getting panic emails from the big manufacturers/ suppliers telling me time is running by and we have to change to R32 and the world is ending etc, but R410a is not banned, not for a long time yet.

    a) R32 is not suitable for the larger systems (too risky) and the VRF/vrv manufacturers are shifting to chilled water equipment to follow the price-conscious consultants/customers. That is how it is.

    b) The smaller systems/splits come with a R410a charge that mostly satisfies the install, in which case R410a is not a problem for the installer. After that, how often does one need to replace the gas? Maybe after 5yrs, or longer. And then, customer has to pay for what, 2-3kg of gas? Hardly a bank loan is it?

    Seems strange we are being panicked and herded to install R32 systems.

  13. #13
    Join Date
    Mar 2015
    Location
    United Kingdom
    Age
    40
    Posts
    14
    Rep Power
    0

    Re: R32 -Use of flares on indoor uniits

    To be honest even fgas regs say braze joints where possible if done properly its less likely to leak ever and a much more secure way of connecting . Yes braze joints do leak but to be honst thats due to poor brazing 9/10 times and the procedure itself . This is why these days when ordering expansion valves they will allways give you brazed type first before flared . I've allways been taught to cut flares on wall mount and braze the pipe esp in heat pumps , i have seen the knuckle go on lots of units because of different modes used and the expand and contraction i always thought it was common practise to braze when possible

  14. #14
    Join Date
    May 2006
    Location
    Sussex
    Posts
    364
    Rep Power
    20

    Re: R32 -Use of flares on indoor uniits

    Just a bit more on the 'slightly flammable R32' ….. Honeywell has produced a refrigerant that can be used in R410a equipment (instead of R410a). It is still being quality-checked for use in aircon systems, as an acceptable replacement for R410a, but indications are that it will pass through those quality checks over the next few months.

    There is vague mention of a minor change to existing (R410a) equipment when changing to this new gas but Honeywell say such costs pale in comparison to changing the existing units/equipment to R32 units.

    The new refrigerant is R466A or ‘Solstice-N41’ and offers greater energy efficiency, a GWP of 733 (slightly more than R32’s GWP of 675), but with ZERO FLAMMABILITY.

    For customers with existing R410a equipment this is good news. If an existing aircon system breaks down and requires a new charge of refrigerant, then instead of suffering the ruinous cost of the rationed R410a refrigerant or having to replace the equipment with R32 units, it might be preferable to instead refill with this new R466A refrigerant (when it is available).

    New systems: If the arrival of R466A could be relied upon – ie a given that it will be on sale next year and that it would meet all its promises about being an inexpensive replacement for R410a refrigerant – then customers could continue to install R410a systems (rather than the slightly flammable R32 systems), knowing that the new R466A will be available by the time that the system might need repairs. Usually, there is (generally speaking) no trouble with an aircon system for at least five years.

  15. #15
    Join Date
    Feb 2005
    Location
    United Kingdom
    Age
    53
    Posts
    56
    Rep Power
    20

    Re: R32 -Use of flares on indoor uniits

    But R410a equipment wont be available as all the manufacturers will have moved away from it by then. They dont have the quota under F-Gas phasedown to continue pre-charging with R410a