    Mar 2005
    Birmingham U.K.
    64
    54
    14
    F Gas certificate for water chiller
    Hi All
    Can someone advise me regarding the paperwork for the chiller below:
    I have a water chiller with 2 refrigerant circuits - each circuit contains 16kg of refrigerant running on R 407c .
    After leak checking the equipment I provide the client with a separate certificate for each circuit, therefore 2 log sheets,- this is done every 12months
    The client has informed me that I should be doing a single log sheet every 6 months because the charge is 32kg which would be 56.77 tonne EQ CO2.
    Have I been doing the log sheets incorrectly?
    Thanks Bob
    May 2012
    54
    1,310
    30
    Re: F Gas certificate for water chiller
    Hi Bob
    You are correct, it is per circuit as long as they are completely separate,
    they can share the same chassis but the circuits must be separated.
    When it was the older 3 Kg weight limit, multi deck manufacturers got
    under the weight limit by putting two smaller systems in, both under
    the 3 Kg.
    Each circuit as you say is 16 Kg so the individual C02 equivalent is
    28 and a bit tonnes so you are correct in your two systems once a year.
    Rob
    Mar 2005
    Birmingham U.K.
    64
    54
    14
    Thanks Rob for for the answer
    May 2012
    54
    1,310
    30
    Unless they insist on paying you lots of money to do the second visit
    Rob