    Calculating needed cooling power



    I am currently doing a project(it is a part of my education) on a cooling unit for a chemical company. They have removed a big load an old screw compressor and it is currently running on a 7%-17% load:/ That is not good..

    I am doing some calculations on some possible options to replace this old screw compressor.

    The screw compressor is in 10 out of the 12 months supplying some chemical reactors and it is possible to determine the cooling capacity by measurement. But two months a year they are using the unit to a special production where methanol is to be cooled down to -10°C.

    It has to be cooled from 40°C to -10°C in 210 min. So I am able to calculate an average cooling power to approximately 32 kW.

    I have also been able to calculate the possible heat transfer through the heat exchanger when temperature differens between cooling liquid and the methanol are at its highest there will be no problem in transfering 32 kW. But when I reach -5°C on the methanol I am not able to transfer more than 24kW.

    So my question is. In a mathematical manner. How would you do calculations in this case? I do know that if I install a unit that can deliver more than 32 kW I can transfer more heat in the first period so that i do not have to transfer 32kW through the hole process.

    But how could I prove this in a mathematical way?

    I hope I have made myself understandable, as I find it hard to express myself in english when it become technical. Feel free to ask if there are something that I haven't made clear.



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Calculating needed cooling power

    .

    have also been able to calculate the
    possible heat transfer through the heat exchanger when
    temperature differens between cooling liquid and the
    methanol are at its highest there will be no problem in
    transfering 32 kW. But when I reach -5°C on the methanol
    I am not able to transfer more than 24kW.


    Why can't you transfer as much heat at -5 compared to +40??

    Methanol has more heat energy per Kg at -5 than +40?
    So if the heat is there why can't it be transferred?

    What refrigerant is your primary?

    Regards
    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Calculating needed cooling power

    .

    Oh by the way

    Welcome to the site



    Rob
    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  4. #4
    Join Date
    Sep 2016
    Location
    Danmark
    Age
    37
    Posts
    2
    Rep Power
    0

    Re: Calculating needed cooling power

    Thank you.

    It is a 30% CaCl2 solution running in a cooling jacket on a reactor in which the methanol is located. Is it the cooling jacket which is not able to transfer the heat.
    It is calculated with the formula P=U×A×deltaT. So when delta to between brine and methanol becomes smaller as the methanol cools down. It won't be able to transfer as much heat.