Results 1 to 9 of 9
  1. #1
    Join Date
    Jun 2016
    Location
    Nigeria
    Posts
    64
    Rep Power
    8

    Panasonic 3ton ac



    Good day everybody!
    Panasonic outdoor keeps running and does not stop even while the indoor unit is turned off.

    The outdoor only stop when the main power source breaker is switch off.

    I'm suspecting the indoor board/ panel.
    What could be the problem? Thanks



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Panasonic 3ton ac

    Model numbers might help us to see what system you are talking about

  3. #3
    Join Date
    Jun 2016
    Location
    Nigeria
    Posts
    64
    Rep Power
    8

    Re: Panasonic 3ton ac

    The model number...CS-C28FF
    thanks!

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Panasonic 3ton ac

    Probably a power contactor stuck.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Jun 2016
    Location
    Nigeria
    Posts
    64
    Rep Power
    8

    Re: Panasonic 3ton ac

    Thanks!
    But the indoor takes the power from the power source,
    While the outdoor takes power from the indoor.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Panasonic 3ton ac

    As Brian says, it is probably a stuck/welded relay. You will need to trace the power from the indoor pcb with a multimeter.

  7. #7
    Join Date
    Jun 2016
    Location
    Nigeria
    Posts
    64
    Rep Power
    8

    Re: Panasonic 3ton ac

    Thanks!
    I will do just that

  8. #8
    Join Date
    Feb 2015
    Location
    India
    Posts
    43
    Rep Power
    0

    Re: Panasonic 3ton ac

    C2423848-0506-4990-8F7D-F9CF89A4B62C.jpgBrian is right. The mag. relay must have stuck in make position, once you tap it, it may start working but later it would again start giving you the problem. Find the picture of the power card, I hope it helps.
    I maintain, everything I have, myself.

  9. #9
    Join Date
    Jun 2016
    Location
    Nigeria
    Posts
    64
    Rep Power
    8

    Re: Panasonic 3ton ac

    Thanks a lot Vikky