Results 1 to 9 of 9
    Jun 2016
    Nigeria
    29
    Panasonic 3ton ac
    Good day everybody!
    Panasonic outdoor keeps running and does not stop even while the indoor unit is turned off.
    The outdoor only stop when the main power source breaker is switch off.
    I'm suspecting the indoor board/ panel.
    What could be the problem? Thanks
    Oct 2001
    Nottingham UK
    5,115
    42
    Re: Panasonic 3ton ac
    Model numbers might help us to see what system you are talking about
    I'm back on the Pale
    Jun 2016
    Nigeria
    29
    The model number...CS-C28FF
    thanks!
    70
    10,547
    52
    Probably a power contactor stuck.
    Jun 2016
    Nigeria
    29
    Thanks!
    But the indoor takes the power from the power source,
    While the outdoor takes power from the indoor.
    Oct 2001
    Nottingham UK
    5,115
    42
    As Brian says, it is probably a stuck/welded relay. You will need to trace the power from the indoor pcb with a multimeter.
    Jun 2016
    Nigeria
    29
    Thanks!
    I will do just that
    Feb 2015
    India
    42
    C2423848-0506-4990-8F7D-F9CF89A4B62C.jpgBrian is right. The mag. relay must have stuck in make position, once you tap it, it may start working but later it would again start giving you the problem. Find the picture of the power card, I hope it helps.
    I maintain, everything I have, myself.
    Jun 2016
    Nigeria
    29
    Thanks a lot Vikky