Results 1 to 2 of 2
  1. #1
    Join Date
    Jul 2010
    Location
    up norrfff
    Posts
    23
    Rep Power
    0

    Mitsi old unit problems...stumped



    Good day,

    Please could you advise and/or send a process i can check for a PUHZ-RP5VHA.

    Original complaint U6 error so attending engineer ordered power board and compressor. This was replaced and unit work ok for about 6 hours when apparently RCD tripped.

    Compressor meggered ok (500v...more than 20megaohms & no shorts to earth).
    No power board so replaced and no leds lit on control board (no fault codes) although there is power at the control board test point. Mains voltage good, not tripping....it appears that there is not enough dc voltage to control board.....changed resistor....still no joy. I do have 240v at the noise and input to power board. I have swapped over the magnetic contactor from another unit but still no joy.

    I am running out of parts to change on this 14 year old unit.....could a noise board cause this ?

    I will be gratefull for a steer...

    Thanks very much.



  2. #2
    Join Date
    Jun 2014
    Location
    Scotland
    Age
    40
    Posts
    38
    Rep Power
    0

    Re: Mitsi old unit problems...stumped

    14 years old! Just replace the system.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •