    Hey guys, I need some clarification between these 2 data sets.
    I was studying a refrigeration system that uses R404A. I graphed the refrigeration cycle on a P-H Diagram to get a better idea of what was going on. After that, i looked up a Pressure-Temp Chart for R404 and noticed things were not adding up. On the PH Diagram R404 is at 0*F at a pressure of about 50psia, however according the Pressure-Temp Chart for the same refrigerant, @ 0*F P=33.5 psig. Am i missing something here?
    Thanks in advance!
  2. #2
    Brian_UK's Avatar
    Brian_UK is online now Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    70
    Posts
    10,661
    Rep Power
    52
    Re: R404A Pressure-Enthalpy Diagram Properties VS Pressure-Temp Chart Properties
    Only missing about 2.5 psi so not too bad.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015
    Please support http://the100project.net/Home
  3. #3
    Join Date
    Jan 2017
    Location
    usa
    Posts
    6
    Rep Power
    0
    haha actually it turns out it was a little more than 2.5, more like 14.7 psi. I think i have found the discrepancy and it all boiled down to units. The Pressure-Temp table is in psig and the P-H graph is in psia.
  4. #4
    Brian_UK's Avatar
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    70
    Posts
    10,661
    Rep Power
    52
    Quote Originally Posted by milen_d View Post
    Exactly hence my answer.
    Retired March 2015
  5. #5
    Join Date
    May 2012
    Location
    England
    Age
    54
    Posts
    1,345
    Rep Power
    30
    pH charts are always in absolute.
    So they will always be 1 atmosphere
    higher than gauge.
    1 atmosphere = 1 bar = 14.7 psi
    Rob
  6. #6
    Join Date
    Jan 2017
    Location
    usa
    Posts
    6
    Rep Power
    0
    Cool thanks for the help guys! Just one more example of why units are our friends !