Results 1 to 12 of 12
Thread: An odd one..
    Feb 2006
    Hampshire
    59
    13
    An odd one..
    Guys,
    Today I had a quick look at a system which is reported to trip regularly when the weather is cold.
    The outdoor unit is an old(ish) Airedale R407c cuhs heat pump. It's matched to a custom made coil within a ahu.
    Fairly simple system really, each end has a tev and all controls are electro mechanical.
    Anyways..
    Took some readings today, head pressure 180psi and suction 50psi when in heating.
    They seem a bit low to me?
    The system has a llsg which shows clear with no flashing, although obviously in heating it's the liquid return to the outdoor unit from the indoor dx coil.
    I found some old paperwork from previous work which shows it has a charge of 3kg. I looked at the manufacturers spec, measured pipework etc and it would appear it should have 5kg.
    Spec shows 0.6kg base charge (up to 7m) then 28g per metre. Total run was 23m
    The lp switch trips at 0.5 bar. I'm kinda assuming that when the weather is cold, the reduced temp over the outdoor coil is possibly causing the suction to drop to cut out point?
    Would you agree I'm on the right track here with what may be the cause of the trips? I've not looked at this before and today it was 10c and it did not trip, so can't even confirm it was tripping on lp, that's just my guess at this time. I can't test it in cooling, as it supplies a temp critical area.
    The thing that's niggling me, is that a total charge of 5kg seems a lot for what is a fairly small 5kw system.
    Advice appreciated as always.
    Feb 2006
    Hampshire
    59
    13
    Re: An odd one..
    Ok,
    Blonde moment.....
    Base charge is 0.6kg, then add 28g per metre over 7m.
    Therefore the charge should be 1.076kg.
    That's gone the other way now and seems too little.
    The system has 3kg, so taking it back to 1.076 would make it worse?
    5,091
    42
    Re: An odd one..
    Had the same issue with 4 Hitachi splits a few years ago. Definately lp cut out due to low ambients.
    got round it by fitting a stat across the lp switch.
    I'm back on the Pale
    Feb 2006
    Hampshire
    59
    13
    Re: An odd one..
    Thanks Frank,
    Did you see my update?
    10,505
    Re: An odd one..
    Quote Originally Posted by terminator View Post
    Ok,
    Blonde moment.....
    Can you confirm the model number because according to the data the smallest CUHS is a size 2.5 with a base charge of 1.3kg.
    Feb 2006
    Hampshire
    59
    13
    Re: An odd one..
    Hi Brian,
    It's a CUHS2 HEIM.
    I just checked the data I have and still getting 0.6kg as base charge? - Very odd.
    Also worth noting that this was installed with a 3/8 liquid line, where the manual says it should be 1/4.
    5,091
    42
    Re: An odd one..
    Thanks Frank,
    Must have posted before your update.
    Oct 2009
    179
    12
    Re: An odd one..
    Is there a defrost timer on the outdoor unit and does it operate
    Feb 2006
    Hampshire
    59
    13
    Re: An odd one..
    Hi mate,
    Yes, I tested that and it works fine.
    ireland
    47
    1,280
    33
    Re: An odd one..
    Check the AHU isn't running full fresh air on heating, pull the charge and verify weight, is the drier ok, outdoor fan running at 100%?
    Feb 2006
    Hampshire
    59
    13
    Re: An odd one..
    Thanks Al,
    I'll be looking at this again on Friday.
    Will keep this updated.
    Feb 2006
    Hampshire
    59
    13
    Re: An odd one..
    Not ignoring you guys, just not been back to it yet. Been held up with other stuff!!