    I hope somebody will help me for understanding compressor oil test procedure. We are planing to produce reversible heat pumps with combination of ventilation unit.

    Compressor manufacturer advised to make oil tests. A few of them are a little bit unclear for me:
    - I should perform oil test with minimum refrigerant flow (minimum refrigerant flow is when evaporating temperature is minimum and condensing temperature is maximum)

    Question: should I perform this test in both modes (summer/winter)? Or minimum refrigerant flow is only in winter?

    - I should perform oil test with maximum oil circulation degree (maximum oil circulation degree is when evaporating and condensing temperatures are maximum).

    Question: should I perform this test in both modes (summer/winter)? Or maximum circulation flow is only in summer?

    I hope somebody can provide me answers, thank you in advance.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    69
    Posts
    10,444
    Rep Power
    50

    Re: Test procedure

    What sort of test of the oil is required?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015
    Please support http://the100project.net/Home

  3. #3
    Join Date
    Feb 2015
    Location
    Lithuania
    Age
    26
    Posts
    10
    Rep Power
    0

    Re: Test procedure

    Brian, minimum oil level in compressor. Before massive production of units oil tests should be made. For these oil tests, compressor with mounted sight glass is required. Sight glass is mounted into bottom part of compressor and during each testing phase/mode/conditions you can directly see what level is in the compressor. For proper compressor functionality oil level in compressor should be above minimum value all the time.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    69
    Posts
    10,444
    Rep Power
    50

    Re: Test procedure

    I think that you have answered your own question, you look at the oil sight glass to see what the level is.

    Until the compressor is running then the oil does not move, it is up to you to ensure good oil return is achieved when the system is running.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015
    Please support http://the100project.net/Home

  5. #5
    Join Date
    May 2012
    Location
    England
    Age
    53
    Posts
    1,234
    Rep Power
    28

    Re: Test procedure

    .

    Looking at your first post and the last one, if I understand you
    correctly, the test is referring to oil return back to the compressor
    via the suction line.

    Mass flow rates of the refrigerant will affect the oil return so that
    is why the test is done at minimum flow rates (mass flow).

    If the evaporator is below the compressor then traps in the suction
    will be required. The size of the pipe is a factor as well.

    So if it is a reversible heat pump the oil passing round the system
    will have to be calculated and that will mean the oil return must be
    in heating and cooling mode.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..