    Daikin E6 split



    Can any one help on this says the fault could be to much current through the inverter or the compressor being seized need to be prepared before I go to site as it’s a 200 mile round trip what’s the best way to check thank you



  2. #2
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Daikin E6 split

    Quote Originally Posted by eurocooling View Post
    Can any one help on this says the fault could be to much current through the inverter or the compressor being seized need to be prepared before I go to site as it’s a 200 mile round trip what’s the best way to check thank you
    E6 is non inverter compressor seized usually?