    MHI 5/8 service valve



    Hi guys

    The company I work for have about 200 of these units in my area alone ( Fdcva502henar ) and probably over 1500 units in the uk. Speaking to the other engineers we are finding that about 60% of units leak from the 5/8 valve. I actually pressure tested one with ofn, when the pressure got to about 25bar the cap blew off like a bullet. I was so lucky not to be standing in front of the unit. Anyone else have issues like this?

    Thanks



  2. #2
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: MHI 5/8 service valve

    What refrigerant is being used in this equipment,are you not exceeding test pressure.

  3. #3
    Join Date
    Jun 2014
    Location
    Scotland
    Age
    40
    Posts
    38
    Rep Power
    0

    Re: MHI 5/8 service valve

    R410a it's fine at that pressure.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: MHI 5/8 service valve

    These are for R410A!

    What cap has blow off? The one which cover the stem of valve? If that is the case than someone has already tried to stop leak by over-tightening that cap and by doing so deformed the cap and valve winding! O-ring of the valve stem should be changed with correct sized one after refrigerant recovery. You need to make special tool for reshaping original bore of valve deformed from over-tightening of cap and then remove stopping ring before valve stem removal.
    Valve cap is not designed to be 100% gas tight, because material of valve and cap is too hard for that!
    Therefore you need to change O-ring!

    I see that kind of leak all the time! No matter what manufacturer. But not in that magnitude!
    Last edited by nike123; 03-12-2017 at 09:39 PM.

  5. #5
    Join Date
    Jun 2014
    Location
    Scotland
    Age
    40
    Posts
    38
    Rep Power
    0

    Re: MHI 5/8 service valve

    image001.jpg

    Here is a photo, you can see where the brass cap is about to pop
    Attached Images Attached Images

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: MHI 5/8 service valve

    Whatever the problem it should be reported to supplier/manufacturer with evidence of what you have found.
    If a cap blew off it's not fit for purpose.
    If your company buy's so many they probably have a bit of power over them.
    Could you forgive yourself if someone did get injured or killed because of it & you said nothing?

    Interesting as well that you have gauge line on schrader valve, what happens when you remove hose, does it release a bit of refrigerant?
    I thought schrader core depressing tool was the way to go, or pump unit down before removing gauge hose, unless I misunderstand connector you are using.

    http://www.airwholesalers.com.au/ind...product_id=334
    Last edited by RANGER1; 05-12-2017 at 08:16 PM.

  7. #7
    Join Date
    Oct 2007
    Location
    jersey channel islands
    Posts
    187
    Rep Power
    19

    Re: MHI 5/8 service valve

    Must say it looks as it was over tightend at sometime , did see this on a com's room split where the suction pipe had frozen .
    also notice that the outdoor isolator has been wired in pump flex , which will in time degrade and rot depending on the sun