    Carrying out HP trip on Airedale chiller



    Hi guys.

    Have a question in which I'm hoping the more experienced engineers may be able to help me out with.

    I carried out a HP trip test but chiller didn't trip out on HP. It sat at 13.9Bar before going out on compressor overload and condenser fan overload.

    Now this circuit is R134A and appears to have a lack of fridge, although only running at 25%, no flashing sight glass and green, no temp difference across the drier cores, fans working well. The other circuit tripped out as it should.

    The only thing noticeable was the heavily frozen eev.

    Would this possibly be a HP switch or due to the lack of fridge or something else possibly?

    Help appreciated as I'm only new to this game.

    Thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Carrying out HP trip on Airedale chiller

    How did you perform the test?

    Compressor and condenser fan tripping on overload sounds strange to me.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2017
    Location
    Essex
    Age
    44
    Posts
    81
    Rep Power
    7

    Re: Carrying out HP trip on Airedale chiller

    It’s an air cooled pacakge chiller.

    I turned off the fans to carry it out

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Carrying out HP trip on Airedale chiller

    What is the HP switch set at?

    How did the condenser fans trip on overload when they were switched off?

    The EEV may not be controlling properly, it needs checking.

    What is the chiller model number?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    May 2017
    Location
    Essex
    Age
    44
    Posts
    81
    Rep Power
    7

    Re: Carrying out HP trip on Airedale chiller

    Hi Brian

    The HP trip is set at around 16Bar.

    I've no idea, that is what came up on the controller under alarms.

    I know it is short of fridge and that combining with the fact that teh eev is heavily frozen that could of been the issue?

    Airedale OPC850HEDQ14

    Many thanks

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Carrying out HP trip on Airedale chiller

    You need to repair the leak on the system and recharge it correctly before any further fault finding.

    You say it is short of "fridge", what type, under counter, concealed, bottle cooler? Or is it short of refrigerant?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Carrying out HP trip on Airedale chiller

    I always have a set of gauges on when carrying out either a HP or LP trip

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Carrying out HP trip on Airedale chiller

    Quote Originally Posted by Brian_UK View Post
    You say it is short of "fridge", what type, under counter, concealed, bottle cooler? Or is it short of refrigerant?
    Never seen a chiller serving a bottle cooler Brian...lol

  9. #9
    Join Date
    May 2017
    Location
    Essex
    Age
    44
    Posts
    81
    Rep Power
    7

    Re: Carrying out HP trip on Airedale chiller

    Sorry Brian

    I mean short of refrigerant. That’s just a term we seem to use. Thanks though I just thought I’d see if anyone had come across it before.

    Yes frank I had my Bluetooth gauges set on the system also that’s where I got the reading

  10. #10
    Join Date
    Jan 2011
    Location
    London
    Age
    38
    Posts
    43
    Rep Power
    0

    Re: Carrying out HP trip on Airedale chiller

    Hi Fella

    the reason you have the fan overload trip is because you switched the breaker off that will generate an overload alarm. There are inverter fans on theses also
    the chiller will unload @14.0 barg to prevent a high pressure trip in order to trip the chiller
    the best way is to enter the test page and manually load the compressor to 8 steps 100% then switch the fans off then the chiller will trip out on high pressure
    or just lower the software hp setting down to 8.0barg and let it trip on software setting