    Daikin super inverter



    Hi guys, I'm having a issue with a daikin super inverter. It keeps showing a e4 fault. I have decanted the unit and charged by weight. It was all ok. I have checked my pressure transducers and they are fine. I have also changed the board ( swapped from a redundant unit)
    Whenever I arrive it is in a e4 fault (low pressure) when I reset the unit it works fine but the condenser freezes up very quickly.

    I'm guessing I have a restriction or a faulty eev.

    Just like to know your thoughts.

    Thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Daikin super inverter

    Have you checked the temperature sensors?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jun 2014
    Location
    Scotland
    Age
    40
    Posts
    38
    Rep Power
    0

    Re: Daikin super inverter

    Yeah I've changed the thermistors but again from the redundant unit.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Daikin super inverter

    Quote Originally Posted by Craig Johnston View Post
    Whenever I arrive it is in a e4 fault (low pressure) when I reset the unit it works fine but the condenser freezes up very quickly.
    I assume that you are in 'Heating' mode?

  5. #5
    Join Date
    Jun 2014
    Location
    Scotland
    Age
    40
    Posts
    38
    Rep Power
    0

    Re: Daikin super inverter

    Yeah. It's on a biddle door curtain so the shop would kill me if I put it in cooling.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Daikin super inverter

    Do you have a full model number?

  7. #7
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Daikin super inverter


  8. #8
    Join Date
    Jun 2014
    Location
    Scotland
    Age
    40
    Posts
    38
    Rep Power
    0

    Re: Daikin super inverter

    Tested the low pressure sensor already. Mod rzq250c7y1b biddle is UK.city m-200-dk-f

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Daikin super inverter

    Have you checked that the Biddle unit is clean and with the correct airflow.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  10. #10
    Join Date
    Jun 2014
    Location
    Scotland
    Age
    40
    Posts
    38
    Rep Power
    0

    Re: Daikin super inverter

    Yeah filters and coil clear with great airflow

  11. #11
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    138
    Rep Power
    21

    Re: Daikin super inverter

    What is the outdoor temperature?
    Last edited by narkom; 01-12-2017 at 10:04 AM.

  12. #12
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Daikin super inverter

    On page 24 the piping diagram shows an expansion valve feeding the outdoor coil in heating mode. This may be starving your coil and causing the low pressure fault http://www.daikintech.co.uk/Data/Spl...B_Databook.pdf

  13. #13
    Join Date
    Jun 2014
    Location
    Scotland
    Age
    40
    Posts
    38
    Rep Power
    0

    Re: Daikin super inverter

    Cheers Frank, thought it was the expansion valve. I'll replace it and keep you updated.