Results 1 to 22 of 22
  1. #1
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Daikin mono bloc low temperature



    Hi we have a client and his system cuts off after two hours this is on heating 11 radatiors on a low temperature this is only 6 months old what would cause this to cut off if you could help please



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    75
    Posts
    11,192
    Rep Power
    60

    Re: Daikin mono bloc low temperature

    Are there any fault codes showing?

    What are the operating temperatures?

    Does it restart?

    We can't see the system so some help needed.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Daikin mono bloc low temperature

    Hi the temp is on 55 no fault codes are coming up also I switch back on and this will run another 2 hours

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    75
    Posts
    11,192
    Rep Power
    60

    Re: Daikin mono bloc low temperature

    Slowly pulling teeth he continues...

    Please give us some data to work with.

    A set point of 55°C tells us very little about what is happening.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Daikin mono bloc low temperature

    Hi

    we have 11 rads of one Daikin monobloc of 16kw 3 phase our outdoor temp at night is 12 degrees with day time of 24 when we run the system at 40 degrees from controller works great when this is on 55 degrees the system shuts off check for and air all ok, water ok hope this helps uand thanks for your time

  6. #6
    Join Date
    Dec 2008
    Location
    UK
    Posts
    568
    Rep Power
    24

    Re: Daikin mono bloc low temperature

    Diificult to second guess this one. There are a few possibilities that it could be and I would not want to jump to an incorrect conclusion.
    As it would appear to possibly be time related, check that there are no strange timer settings invoked.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  7. #7
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Daikin mono bloc low temperature

    Hi

    i checked all timers

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Daikin mono bloc low temperature

    You should read service manual and find what function alarm is having 2 hours delay before alarm is activated!

    For further help, you should post model name!

  9. #9
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Daikin mono bloc low temperature

    I read the service Manuel also it a 16 kw Daikin mono bloc heating only

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Daikin mono bloc low temperature

    Quote Originally Posted by eurocooling View Post
    Daikin mono bloc heating only
    That is not model name!

  11. #11
    Join Date
    Dec 2008
    Location
    UK
    Posts
    568
    Rep Power
    24

    Re: Daikin mono bloc low temperature

    The model number can be found on the data plate, which is usually on the external surface of the unit.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  12. #12
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Daikin mono bloc low temperature

    Hi the model number is EDHQ016BB6V3
    heating only hope that helps 3phase so well

  13. #13
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    75
    Posts
    11,192
    Rep Power
    60

    Re: Daikin mono bloc low temperature

    Have you checked that the field settings are correct for the installation?

    Have you performed a test run and did it complete satisfactorily?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  14. #14
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Daikin mono bloc low temperature

    Hi I have done a test run all ok since I drop it to 40 it's working really good maybe at 55 with outdoor temp at night of 15 there is a reason why it cut off

  15. #15
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Daikin mono bloc low temperature

    Domestic hot water tank is installed or not?
    What is your 8.01 field setting?

    (b) Heating/cooling or domestic water heating mode can be restricted by schedule timer and/or field settings (4, 5, 8).
    [4-02] Space heating off temperature: outdoor temperature
    above which space heating is turned off to avoid overheating.
    It would be best that you post here all your field settings!
    Last edited by nike123; 15-11-2017 at 07:32 PM.

  16. #16
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    75
    Posts
    11,192
    Rep Power
    60

    Re: Daikin mono bloc low temperature

    How does it perform if you run it under weather compensation?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  17. #17
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Daikin mono bloc low temperature

    It run great at 40 it's very rare we gets temps below 6 degrees

  18. #18
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    75
    Posts
    11,192
    Rep Power
    60

    Re: Daikin mono bloc low temperature

    So you are setting at 40 not under weather control?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  19. #19
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Daikin mono bloc low temperature

    Yes it's set at 40 and working perfect if I set at 55 cuts off

  20. #20
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Daikin mono bloc low temperature

    Quote Originally Posted by eurocooling View Post
    Yes it's set at 40 and working perfect if I set at 55 cuts off
    If that's the case, I would be looking at the condensing side of the system

  21. #21
    Join Date
    Dec 2008
    Location
    UK
    Posts
    568
    Rep Power
    24

    Re: Daikin mono bloc low temperature

    It could be reduced water flow or potentially an air bubble causing reduced flow. if the system works fine when set at 40degC, there may be insufficient heat transfer at the elevated temperature. There should be a minimum deltaT of 5degC. 55degc at right at the top end of the capability of the unit. Possibly the heat loss of the system and building prevents the system from achieving 55degc and the unit may be cutting out on high compressor temperature. This would not necessarily indicate a fault code as the system would eventually stop and then restart after a time period.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  22. #22
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Daikin mono bloc low temperature

    Thanks Hyper

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •