    Re: Sab 128 Problems

    Hi
    put it in manual position
    than push up load see what happen
    if you capacity goes up and AMPS move to high
    you check your setting
    if not
    check suction filter and all valves

  2. #2
    Join Date
    Aug 2014
    Location
    Norway
    Age
    54
    Posts
    27
    Rep Power
    0

    Re: Sab 128 Problems

    I have checked the suction filter. It was OK. I also tried to put it in manual position. When I pushed upload, the capasity went up to 100 %. But the amps did not rise. And the suctiongas temperature did not go down. Every other values were OK, such as oilpressure, oiltemp, suctionpressure etc. It seems like the compressor shows 100 % capasity, but only runs in 10-20% capasity. The slide calibration is also OK. I think there might be someting wrong with the slide, showing 100 %, when it maybe is 10-20%, I don`t know.