Re: Sab 128 Problems
Hi
put it in manual position
than push up load see what happen
if you capacity goes up and AMPS move to high
you check your setting
if not
check suction filter and all valves
-
07-11-2017, 09:40 AM #2
Re: Sab 128 Problems
I have checked the suction filter. It was OK. I also tried to put it in manual position. When I pushed upload, the capasity went up to 100 %. But the amps did not rise. And the suctiongas temperature did not go down. Every other values were OK, such as oilpressure, oiltemp, suctionpressure etc. It seems like the compressor shows 100 % capasity, but only runs in 10-20% capasity. The slide calibration is also OK. I think there might be someting wrong with the slide, showing 100 %, when it maybe is 10-20%, I don`t know.