    Sanyo H04 Fault Code
    Hi Everyone, does anyone know what the fault code H04 on a a Sanyo vrf is, l contacted Panasonic and they didn't know ,
    Many Thanks,
    Skilts
  2. #2
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36
    Re: Sanyo H04 Fault Code
    I looked on the google and got protective thermostat for scroll compressor 1.
    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.
  3. #3
    Join Date
    Aug 2009
    Location
    england
    Age
    66
    Posts
    31
    Rep Power
    0
    Thanks Andy,
    I think its crazy that Panasonic don't know,
    Skilts
  4. #4
    Join Date
    Apr 2008
    Location
    Age
    49
    Posts
    1,023
    Rep Power
    36
    Yes, you would have thought if anyone knew it would be the manufacturer, think it depends on who you speak to when you get through really.
    If you manage it, Tony Duffy is the man if he's still there. But tricky to get hold of, probably made a rod for his own back knowing too much!
    Cheers,
    Andy.
  5. #5
    Join Date
    May 2006
    Location
    Hayling Island, UK
    Age
    60
    Posts
    143
    Rep Power
    21
    Hi Sklitz.
    Sanyo H04 =
    Compressor 1 has a discharge temperature in excess of 115°C
    Most common reason is low gas charge, or high diversity or maybe faulty discharge sensor.
    I was the last Tech Manager at Sanyo AC, and now work for an ex-Sanyo (now Panasonic) distributor ESS Aircon in Sutton Surrey so if you need help look us up and give me a buzz. We can supply Sanyo parts too.
    Cheers
    Loops (aka Lewis)