    Refrigerant charge



    Hello, Is there any way of finding the charge/volume of a system?, say there's been a leak, it's been fixed, and now you want to top it up.

    Cheers,



  2. #2
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Refrigerant charge

    try and find an Info plate, if no info plate then ya got me, I have the same problem with a twist lol.

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Refrigerant charge

    Top up until reaching spec subcooling.

  4. #4
    Join Date
    Aug 2005
    Location
    iraq
    Age
    67
    Posts
    130
    Rep Power
    19

    Re: Refrigerant charge

    no.....
    untill you get 3-5 c super heating
    afeef

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Refrigerant charge

    Superheating can be varied depending on the TXV adjustment. Refrigerant charge must be checked against subcooling, not superheating.

  6. #6
    Join Date
    Aug 2005
    Location
    iraq
    Age
    67
    Posts
    130
    Rep Power
    19

    Re: Refrigerant charge

    but the most important term is the superheating ,
    the effecincy of system is depend upon it , the life of compressor depending upon it also
    thanks no neck name

  7. #7
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Question Re: Refrigerant charge

    How many kW on which evaporation temperature?And type of machine also?Which refrigerant you use?

    Renato

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Refrigerant charge

    Quote Originally Posted by afeef
    but the most important term is the superheating ,
    the effecincy of system is depend upon it , the life of compressor depending upon it also
    thanks no neck name
    Of course.

  9. #9
    Join Date
    May 2006
    Location
    China
    Posts
    17
    Rep Power
    0

    Re: Refrigerant charge

    1. check the compressor current of a good equipment ( the same working conditions)
    2. take it as reference and charge the problem equipment.

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Refrigerant charge

    This was already on this forum but charging by current is completely wrong.
    I should say, first subcooling and cross-check also superheat.
    But you can't predict this on forehand.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Refrigerant charge

    Keep adding gas untill the sight glass fills up (or your bottle runs out..lol)

    If your comp gets covered in ice then start to runnnnnn.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  12. #12
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Refrigerant charge

    My vote is on sight glass, I winged it and did just that on my totally pieced together from archaic parts system and bang, hit -34 under load using R-290 and a 1/2ton R-12 TXV under load, and interestingly enough didn't take much extra gas to get it full

  13. #13
    Join Date
    Aug 2005
    Location
    iraq
    Age
    67
    Posts
    130
    Rep Power
    19

    Smile Re: Refrigerant charge

    Quote Originally Posted by The MG Pony
    My vote is on sight glass, I winged it and did just that on my totally pieced together from archaic parts system and bang, hit -34 under load using R-290 and a 1/2ton R-12 TXV under load, and interestingly enough didn't take much extra gas to get it full
    sight glass give you the approximate amount of charge, it can help you monitoring your a/c system from leackage
    but not to determine the exact refrigerent needed .
    afeef

  14. #14
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Refrigerant charge

    Ya I know that, but for a good fast fix it does the job marvellously

  15. #15
    Join Date
    Dec 2005
    Location
    Johor
    Age
    62
    Posts
    151
    Rep Power
    19

    Re: Refrigerant charge

    Hi Nui

    If in doubt than go back to basic.Check on the spec or info on the nameplate of the unit like a few of our members recommended. Reclaimed the refrigerant performing liquid transfer, weigh the charge and add the necessary amount short.

    Good luck mate.

  16. #16
    Join Date
    Nov 2005
    Location
    USA
    Posts
    211
    Rep Power
    19

    Re: Refrigerant charge

    My vote is on sight glass, I winged it and did just that on my totally pieced together from archaic parts system and bang, hit -34 under load using R-290 and a 1/2ton R-12 TXV under load, and interestingly enough didn't take much extra gas to get it full
    1/2 ton unit using R290???
    "If Hannah was an air handler, I would be a condensing unit so I could open her TXV and pump my refrigerant through her coils." - a HVAC friend of mine

  17. #17
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Refrigerant charge

    Why not?, in reality the whole thing is a real hack job of a unit that I build whilst I am building the "real" system.

    "The real" System I'm making will be using R-134a, I may use a mix or R-134a and R-600 to improve its efficiency.

  18. #18
    Join Date
    Jan 2002
    Location
    Mirfield
    Age
    46
    Posts
    32
    Rep Power
    0

    Re: Refrigerant charge

    You could be very technical about the situation and work out the total volume of the different phases!

    :0
    j p g

Similar Threads

  1. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  2. Calculating refrigerant charge
    By Consultant in forum Refrigerants
    Replies: 2
    Last Post: 10-05-2005, 03:39 PM
  3. Refrigerant Reclamation
    By herefishy in forum Commercial
    Replies: 6
    Last Post: 23-07-2003, 08:19 AM
  4. refrigerant charge
    By pirestani in forum Refrigerants
    Replies: 1
    Last Post: 02-06-2002, 02:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •