tk md200 runs fine on electric but wont start on diesel, code 35
when I start up the controller on diesel it comes on, doesn't buzz or prime, no fuel pump engage, just flashes code 35. I checked all the fuses and they are fine, I tried a new fuel solenoid and now I was advised to swap out the MP.
just wondering if the problem is in the MP or maybe something less expensive that I missed.
-
28-10-2017, 12:10 PM #2
Re: tk md200 runs fine on electric but wont start on diesel, code 35
Check all connections at battery and the main fuse which is normally at the battery.
-
30-10-2017, 10:27 PM #3
Re: tk md200 runs fine on electric but wont start on diesel, code 35
The connections/voltage at the battery are all good. Just wondering if there's anything I could check before swapping out a board for $900.
-
30-10-2017, 10:49 PM #4
Re: tk md200 runs fine on electric but wont start on diesel, code 35
If it has a remote switch fitted on the unit replace it or link it out they can give issue's
-
31-10-2017, 07:28 PM #5
Re: tk md200 runs fine on electric but wont start on diesel, code 35
I was double checking the fuses/voltages at the board and managed to start it on diesel. It ran for 10 mins and shut down to code 63/84. Waited a few mins and cleared codes, started up and ran 10 minutes before shutting down to code 35.
-
31-10-2017, 09:34 PM #6
Re: tk md200 runs fine on electric but wont start on diesel, code 35
Did you locate and replace or bypass that remote switch,and are the connections fuses going to stop run solenoid bad earth's can give all kinds of issues
-
31-10-2017, 10:06 PM #7
Re: tk md200 runs fine on electric but wont start on diesel, code 35
Not familiar with a remote switch, do you mean the box door sensor?
-
01-11-2017, 12:32 AM #8
Re: tk md200 runs fine on electric but wont start on diesel, code 35
It's a switch fitted to the unit frame it's purpose is so you can stop the unit without climbing off the cab roof it's normally fitted on the right hand side as you look at the unit from the front.
-
02-11-2017, 06:57 PM #9
Re: tk md200 runs fine on electric but wont start on diesel, code 35
Oh, the guy who trained me always called that the master switch lol.
I pulled a MP out of another unit to test against this one and the unit started right up on diesel.
The bad board would not show voltage to the fuel solenoid wire on the board, I think the diesel circuit was just worn.
Thanks for the help.