    May 2017
    Essex
    38
    35
    Star delta motor issues
    Afternoon guys.
    Wondered if I could have some help please.
    Have wired up a new motor in the star delta configuration.
    connections at the motor are fine I believe.
    Now when motor is turned on main and star operate, then few seconds later, star kicks out and delta pulls in.
    The main is still in but now the motor stops.
    Any ideas as im going mad here thinking why?
    Many thanks
    May 2017
    Essex
    38
    35
    Re: Star delta motor issues
    Right. There's no voltage coming from the bottom on the contactor even though there is voltage at 1 3 5, just not 2 4 6.
    Coil has been pulled in but nothing going through. Assuming this is my issue.
    63
    4,529
    38
    You seem to have found the issue.
    Good Luck Grizzly
    10,510
    Always check a star/delta starter with a meter before connecting the expensive motor.
    May 2017
    Essex
    38
    35
    Hi Brian.
    It’s ok I found the issue. On the delta side I had 2 wires wrong way round. No expensive bangs or anything so all good. Thanks.
    10,510
    Well done.
