    Climaveneta



    Hey guys,

    Got a climaveneta model FOCS LN 2652.
    According to some manuals I have the refrigerant charge is 136KG's for the chiller.
    The name plate on the chiller is faded however, I though I could make out that circuit 1 was 50KG's and circuit 2 55KG's

    Inside the panel, someone also wrote this, but I cannot find a total charge of 105KG's in any manual.

    Got to charge circuit 2 tomorrow, as it lost it's charge and I now have the leak fixed.

    Any ideas or anyone got a manual that would confirm my 105KG's?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Climaveneta

    Have to agree, all that I have found state 136kg R134a.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Climaveneta

    That's a lot of refrigerant! The invoice will be massive