    Oct 2017
    2
    What is a typical range for discharge superheated degree in VRF systems?
    Hi -
    My question is in the title, what is a typical range for discharge superheated degree in VRF systems in cooling mode only? By discharge superheated degree I mean the difference between the discharge pipe temperature and condensing temperature.
    Thank you for your help!
    Apr 2008
    Southampton, England
    49
    1,045
    35
    Re: What is a typical range for discharge superheated degree in VRF systems?
    Condense around 40°C, discharge pipe below 100°, probably somewhere around 80°, give or take a bit.
    5,733
    The discharge gas temperature can range anywhere between 55C up to 100C, depending on load and ambient temperature.
    The inverter compressor safety normally kicks in around 106C by backing off the hz
    Condensing temperature is normally ambient + 15K
    Sep 2009
    Iran
    66
    672
    1
    it is depends to our design in system
    and it is different in what kind of compressor you have
    is it recips or screw
    our outlet pressure is related to our ambient temp and our condenser type (air cooled or water cooled or evaporator condenser ) from that we can find our out let temp from condenser
    air cooled = ambient temp + 6 t0 10 c
    water cooled = ambient + 5 C
    also out let temp in recips compressor related to how cylinders is cooled and oil cooler temp
    Also our gas and our suction pressure is very important
    in PH diagrams if it goes down our temp goes to high side .
    Oct 2017
    2
    Thanks a lot!
Tags for this Thread