    What is a typical range for discharge superheated degree in VRF systems?



    Hi -

    My question is in the title, what is a typical range for discharge superheated degree in VRF systems in cooling mode only? By discharge superheated degree I mean the difference between the discharge pipe temperature and condensing temperature.

    Thank you for your help!



  2. #2
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,044
    Rep Power
    35

    Re: What is a typical range for discharge superheated degree in VRF systems?

    Condense around 40°C, discharge pipe below 100°, probably somewhere around 80°, give or take a bit.

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: What is a typical range for discharge superheated degree in VRF systems?

    The discharge gas temperature can range anywhere between 55C up to 100C, depending on load and ambient temperature.
    The inverter compressor safety normally kicks in around 106C by backing off the hz

    Condensing temperature is normally ambient + 15K

  4. #4
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: What is a typical range for discharge superheated degree in VRF systems?

    Hi
    it is depends to our design in system
    and it is different in what kind of compressor you have
    is it recips or screw
    our outlet pressure is related to our ambient temp and our condenser type (air cooled or water cooled or evaporator condenser ) from that we can find our out let temp from condenser
    air cooled = ambient temp + 6 t0 10 c
    water cooled = ambient + 5 C
    also out let temp in recips compressor related to how cylinders is cooled and oil cooler temp

    Also our gas and our suction pressure is very important
    in PH diagrams if it goes down our temp goes to high side .
    Last edited by mbc; 12-10-2017 at 04:47 PM.

  5. #5
    Join Date
    Oct 2017
    Location
    USA
    Posts
    2
    Rep Power
    0

    Re: What is a typical range for discharge superheated degree in VRF systems?

    Thanks a lot!