    dose it make a difference if txv power head is upside down[on bottom]?



  2. #2
    Join Date
    Aug 2014
    Location
    UK
    Age
    69
    Posts
    401
    Rep Power
    16

    Re: troubleshooting

    Hi markep
    Functionally the answer is no, but if the system is dirty then there is a chance that system debris could cause the orifice push pins to stick or even damage the diaphragm in exceptional circumstances.
    Most fridge valves will work upside down, the only exception is the solenoid valve which must never be mounted upside down.
    Valves have an engineered flow path which helps to self clean the valve in a normal configuration,but in an upside down configuration system debris can become trapped in the mechanical moving parts of the valve ,servo valve types are more susceptible to problems
    In solenoid valves if the armature tube becomes contaminated with system debris or oil preventing the armature from lifting this will cause the coil to burn out.
    It's advisable to get the valve manufacturers opinion on the install as it may affect the warranty,
    Providing the system is clean with a good quality filter drier fitted you should have no problems, as I've seen many valves in this position working.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    51
    Posts
    6,075
    Blog Entries
    6
    Rep Power
    30

    Re: troubleshooting

    Everything about that is on the installation manual of the respecting valve!
    Now, when I am officialy citizen off EU, I am looking for decent job! For any job offer please check my profile!

  4. #4
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    306
    Rep Power
    14

    Re: troubleshooting

    There is NO direct prohibition in the installation manuals to install a TXV upside down.

  5. #5
    Join Date
    Sep 2009
    Location
    Iran
    Age
    60
    Posts
    431
    Rep Power
    11

    Re: troubleshooting

    Hi

    main thing of DX valve is position of bulbs on the suction line and upside and downside and bulb should be after equlizning pipe and insulation bulb on the suction pipe


    http://products.danfoss.com/productr...fice/t-2-te-2/