Thread: troubleshooting
    Jun 2014
    usa
    7
    troubleshooting
    dose it make a difference if txv power head is upside down[on bottom]?
    Aug 2014
    69
    427
    Re: troubleshooting
    Hi markep
    Functionally the answer is no, but if the system is dirty then there is a chance that system debris could cause the orifice push pins to stick or even damage the diaphragm in exceptional circumstances.
    Most fridge valves will work upside down, the only exception is the solenoid valve which must never be mounted upside down.
    Valves have an engineered flow path which helps to self clean the valve in a normal configuration,but in an upside down configuration system debris can become trapped in the mechanical moving parts of the valve ,servo valve types are more susceptible to problems
    In solenoid valves if the armature tube becomes contaminated with system debris or oil preventing the armature from lifting this will cause the coil to burn out.
    It's advisable to get the valve manufacturers opinion on the install as it may affect the warranty,
    Providing the system is clean with a good quality filter drier fitted you should have no problems, as I've seen many valves in this position working.
    Split Croatia
    6,106
    7
    30
    Re: troubleshooting
    Everything about that is on the installation manual of the respecting valve!
    Sep 2009
    Iran
    482
    12
    Re: troubleshooting
    main thing of DX valve is position of bulbs on the suction line and upside and downside and bulb should be after equlizning pipe and insulation bulb on the suction pipe
    http://products.danfoss.com/productr...fice/t-2-te-2/