    chilled water pump befor or after chiller?



    Hi everybody,
    does anybody know exactly where should the chilled water pumps must be installed in a chilled water plant? i mean should they be befor chiller or after it? and why?
    thank you everyone



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: chilled water pump befor or after chiller?

    Sucking from the system and discharging into the heat exchanger. Flow control after the heatexchanger on the discharge line.

  3. #3
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: chilled water pump befor or after chiller?

    Hi
    Also in all pump's our mechanical action give us heating (inlet temperature is lower than out let )
    So it is better we suck from system and pump to evaporator
    And viscosity of cold water is more than hot water
    And in efficiency we have a little difference between them

    Expantion tank should be in suction line

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: chilled water pump befor or after chiller?

    Quote Originally Posted by chemi-cool View Post
    Sucking from the system and discharging into the heat exchanger. Flow control after the heatexchanger on the discharge line.
    Spot on Chemi!
    Grizzly
    Despite the High Cost of Living it still remains Popular!

  5. #5
    Join Date
    Mar 2005
    Location
    u.a.e
    Age
    68
    Posts
    171
    Rep Power
    20

    Re: chilled water pump befor or after chiller?

    Before chillers, this will provide positive pressure to the chillers and also pump strainer will keep dirt off from chillers water side tubes.

  6. #6
    Join Date
    May 2017
    Location
    Iran
    Posts
    5
    Rep Power
    0

    Re: chilled water pump befor or after chiller?

    thanks everybody for answers.
    but if we want to compare these two condition based on the possibility of cavitation isnt it better to put the pumps after chiller where the temp is lower and possibility of cavitation is less?

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: chilled water pump befor or after chiller?

    Cavitation has nothing to do with place of the pump. It has a lot to do with the pump metal qality and cleanles of tha water from small particles and sand.

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: chilled water pump befor or after chiller?

    Pump cavitation can occur on either side of the pump due to incorrect pressures causing low suction pressure or high discharge pressure.

    Always maintain clean water and water strainers also ensure that the pump selection is correct.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: chilled water pump befor or after chiller?

    Hi, chiller-001

    Quote Originally Posted by chiller-001 View Post
    thanks everybody for answers.
    but if we want to compare these two condition based on the possibility of cavitation isnt it better to put the pumps after chiller where the temp is lower and possibility of cavitation is less?

    It is better to install pumps before chiller .... because you have a pressure drop within chiller...

    one request: can you, please, upload scheme of your chilled water system ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: chilled water pump befor or after chiller?

    Regarding cavitation, like in boiler heating aplications, pump should be close coupled with expansion vessel and right after it! Expansion vessel is point of no pressure change (PONPC).
    Here is reasoning:
    The wise a55 in me wants to simply ask; 'Why not?'

    Let's see if I can keep this concise...

    For various reasons, in the past, circulators were placed on the return side.

    Newer materials improved the heat resistance of the pumps, and now they can be placed pretty much anywhere in the system.

    The single biggest reason to 'pump away' is to improve the process of removing air from the system.

    When system pressure is higher, air has a greater tendency to stay in suspension in the water.

    The point in the system that the expansion tank is connected is called the "Point Of No Pressure Change" or PONPC.

    The system pressure is HIGHEST at the DISCHARGE side of the circulator pump, and LOWEST at the SUCTION side.

    When a system is configured such that the pump is pumping TOWARD the PONPC, then when the pump is running, it SUBTRACTS pressure from the rest of the system, and vice versa, when it is pumping AWAY from the PONPC, it ADDS pressure to the rest of the system.

    The AIR ELIMINATION DEVICE should ALSO be placed at the PONPC, so that when pumping away, the air elimination device is at the lowest pressure point in the system. And the rest of the system is at a higher pressure.

    The net result is that the air in the water more easily travels through the system, remaining dissolved in the water (or smaller bubbles because they are 'squeezed' more by the higher pressure), and are more easily 'caught' by the air elimination device at the lowest pressure point in the system.

    Also, HOT water has less capacity to hold air. If the PONPC also happens to be on the HOT SUPPLY side of the boiler, air elimination becomes another bit easier to achieve.

    Not concise really, but hope it helps!

    Also good to read this: http://www.reflex.de/fileadmin/user_...usruestung.pdf

    http://www.doityourself.com/forum/bo...pump-away.html
    Last edited by nike123; 05-10-2017 at 08:28 PM.