    Dont know if anyone has had the same problem but intermittently they system blocks causing the capillary to frost back passed the filter to the condenser which causes the bottom couple of rows on the condenser to sweat. It has recently had a new compressor and filter drier,evacuated and recharged. It can be switched off for a while then switched back on and it works for a while. Any ideas guys.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    69
    Posts
    10,441
    Rep Power
    50

    Re: Zoin serveover display counter

    Refrigerant type?
    Oil type?
    Why was the compressor changed?
    Oil acid level checked at compressor change?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015
    Please support http://the100project.net/Home

  3. #3
    Join Date
    Dec 2008
    Location
    england
    Age
    70
    Posts
    137
    Rep Power
    9

    Re: Zoin serveover display counter

    Hi Brian. R134a. Compressor was noisy. Oil poe. No burnout.oil ok.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,077
    Rep Power
    42

    Re: Zoin serveover display counter

    R134a is known to block capillaries due to oil floccing
    I'm back on the Pale