    Sep 2017
    India
    28
    5
    Alternate for Carrier 19XR Oil
    Currently we need to replace synthetic oil for Carrier Chiller 19XR. Refrigerant is R134a.
    Oil viscosity grade is ISO 68. Can I use Castrol SW68 as an alternate? or is there any suitable alternate available?
    Sep 2010
    70
    209
    11
    Re: Alternate for Carrier 19XR Oil
    Castrol SW68 is a slideway oil not rated for refrigeration use.
    Brian, retired in Devon.
    Mar 2005
    u.a.e
    171
    14
    19xr is a big and expensive machine, replace only recommended oil from Carrier. It needs to replace once in a year after installation and then after 3/5 years. Frequent oil replacing only required if oil test is negative. This test you have to carry out on yearly bases. With non recommended oil you will face warranty issues.
    Please remember a Rolls Roice must be maintained as a RR and not as a Suzuki.
    Somerset
    64
    4,595
    40
    Some important info. Attached.
    Attached Files Attached Files
    Sep 2017
    India
    28
    5
    @Grizzly, it's a very useful document. Hope this will help us a lot. Thanks for your support.