01-06-2006, 11:10 PM #1
Work or not?
Hi guys,
I have a Zanotti cold room which has a remote cond unit(10m).
The pipe sizes are 3/8 and 5/8 from the cond unit all the way to the evap, but when inside the evap there isn't an expansion valve, there is a short piece of capilary.
Total gas charge should be 850gms. R22
Can't remember the details of cond of evap.
Would this system work?
Chillin
IF AT FIRST YOU DON`T SUCCEED.
DESTROY ALL EVIDENCE THAT YOU TRIED!
and go get a cuppa
-
02-06-2006, 01:24 AM #2
Re: Work or not?
I suppose I would attempt to make it work. First thing to go, if it didn't work might be the cap tubing. I don't know about the condensing unit.. does it have a receiver? Anyway, we remoted equipment on cap tubes in the past and managed to make them work, but if I had it to do over, I would make sure I had a TEV and a condensing unit with an adequate receiver for a complete pumpdown of the system.
-
02-06-2006, 06:39 AM #3
Re: Work or not?
Sure, why shouldn't it work. If the manufacturer had selected it that way, then it will work.
It's of course a cheap solution.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
02-06-2006, 08:53 AM #4
Re: Work or not?
Hi peter, I don't think it was ment to be like this, I think it was suposed to have the cond unit on the roof of the cold room.
Hi Dan, There is no reciever, and the cond fan runs without a presure control, (it overcondenses).
I went to this and it was cold outside, the suction was in a vacuum because all the gas was sitting in the condesor.
I fitted a presure control on the fan, but this makes the comp overheat and cut out. So I took it back off agian.
ChillinIF AT FIRST YOU DON`T SUCCEED.
DESTROY ALL EVIDENCE THAT YOU TRIED!
and go get a cuppa
-
02-06-2006, 07:39 PM #5
Re: Work or not?
What type of compressor is used? Unithé Hermétique?
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
02-06-2006, 08:24 PM #6
Re: Work or not?
Originally Posted by Peter_1
This product is simalar to it, but its R404 and mine is R22.
http://www.zanotti.it/english/Dep%20...ock%20SP_O.pdf
Or
http://www.zanotti.it/Dep%20PDF_IT/ByBlock_SP_O.pdf
I really need to know if you can feed a capilary with a 3/8 (10 meters) liquid line.
ChillinIF AT FIRST YOU DON`T SUCCEED.
DESTROY ALL EVIDENCE THAT YOU TRIED!
and go get a cuppa
-
02-06-2006, 08:31 PM #7
Re: Work or not?
Sure, you can do it without a problem.
But make your liquid line as small as possible and don't overfill it.
Cover eventually the condensor a litlle bit to simulate summer conditions.
Fill it till SH and SC are within range and LP and HP are OK.
Do you need some help with the line selection? What capacity do you have actually?It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
02-06-2006, 08:37 PM #8
Re: Work or not?
Do you need some help with the line selection? What capacity do you have actually?
I will get the all the info next week and post it for you here so you know exactly what I am talking about.
Thanks Peter.
ChillinIF AT FIRST YOU DON`T SUCCEED.
DESTROY ALL EVIDENCE THAT YOU TRIED!
and go get a cuppa
-
03-06-2006, 07:44 AM #9
Re: Work or not?
usually the use of tev is for capacities more than 3 tons,(10.5kw), in your cold stor it is less than that ,
why you are worried ?
best of luck
afeef
Similar Threads
-
Work Experiance/Trainee....HELP
By Darren wright in forum TrainingReplies: 3Last Post: 01-11-2010, 05:07 PM -
Prison vs Work
By Abe in forum Chit Chat & Service StoriesReplies: 11Last Post: 06-09-2010, 08:47 PM -
part p
By eggs in forum ElectricalReplies: 25Last Post: 15-11-2007, 08:55 PM -
Mitsibishi VRV System 8 out of 10 units work
By moondawn in forum Air ConditioningReplies: 5Last Post: 29-09-2005, 11:02 PM -
Desperate to work
By nomiracle in forum TrainingReplies: 21Last Post: 29-06-2005, 11:41 PM