    Co2 moisture and acid elevated



    Hi, my question/questions; I have 2 co2 trans critical system that has returned a higher than specified water content in an oil analysis and I have been told not to bother to change the liquid line driers and instead put liquid line drier cores in the suction which I did and waited 2 weeks and retested, one system water/acid increased and the other decreased? Im thinking possibly one was contaminated in the sampling process? But seeing the level is still high I changed the drier cores once more and on removing the drier cores what struck me was the cores are now orange! So can anyone confirm that it is indeed a wast of time changing the LLD and possibly tell how the drier cores turned orange?

    Cheers



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Co2 moisture and acid elevated

    .

    Not sure why they are orange but drier cores are driers
    and if there is contamination inside then they need to be
    replaced in both sides of the system.

    Acid burn outs in the suction and high capacity in the liquid.

    Change more regularly untill clear.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Co2 moisture and acid elevated

    Quote Originally Posted by Rob White View Post
    .

    Not sure why they are orange but drier cores are driers
    and if there is contamination inside then they need to be
    replaced in both sides of the system.

    Acid burn outs in the suction and high capacity in the liquid.

    Change more regularly untill clear.

    Rob

    .

    Rob, if possible change oil as well at same time as driers?

  4. #4
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Co2 moisture and acid elevated

    Quote Originally Posted by RANGER1 View Post
    Rob, if possible change oil as well at same time as driers?
    Yep, agreed :-)

    Good point.

    Depending on pack type, some have oil filter / strainer inside the oil separator.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..