    Oil level on Maneurop MTZ80?



    Fixed a leak on a MTZ80 that had a crack in the discharge line just after compressor and it lost some of it's oil. I added some (maybe 700cc of 1800cc total capacity) but I think it is still pretty low on the sight glass. There is another unit running side by side and it too seems to be low on oil. What is normal level on these when running and when they're off? I can just barely see the level at the bottom of the glass and when it's running it kind of splashes around that low level. Should I add more? Any good tips on how to add oil without evac the compressor and pump it through the oilplug?



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Oil level on Maneurop MTZ80?

    You need an oil pump to fill it up again. Maneuropu compressors are sensitive to low oil level.

  3. #3
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Oil level on Maneurop MTZ80?

    The oil charge for Maneurop reciprocating compressors is 1 litre per cylinder i.e. The single cylinder machines need 1 litre ,the 2 cylinder 2 Litres and the 4 cylinder 4 litres. The oil level when running should be around the 1/2 to 3/4 sightglass level. The level will change slightly from running to standstill due to the vortex effect inside the shell when the compressor is running. When the oil level drops to the bottom of the glass or just slightly lower then you are in danger that the oil level is lower than the crankshaft oil pick up point which will quickly cause the machine to run without lubrication and the connecting rods will seize onto the crankshaft and the powerful motor will then break the rods and the compressor will destroy itself. So it is very urgent that the oil levels are topped up to just over the half glass. Also never overfill a compressor with oil as if there is too much oil the crankcase starts to fill up were the connecting rods and crankshaft and piston are spinning at 3000 revolutions per minute and hydraulic damage can take place to this motion work.
    Each time the compressor starts oil leaves the compressor housing and enters the system ,the system run time and pipe work design should allow for this oil to return back to the compressor. In the U.K the MTZ 80 compressor is mostly used on close control computer rooms etc where the compressor short cycle this leads to low oil levels and also discharge pipe fractures and I've even seen situations where the short cycling has broken off the compressor mount feet. These feet are now reinforced welded to prevent that happening .
    So firstly top up the compressor oil levels and then check the running cycles to make sure they are not being damaged from short cycle abuse.
    I used to carry out the warranty inspections on Maneurop and every MT 80 compressor returned under warranty was low on oil and smashed to pieces . It's an expensive error to make
    There are some Why Compressors Fail articles on Google or the Danfoss web site explaining these situations which I wrote to help prevent these failures or you can pm me and I'll mail the set to you.

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Oil level on Maneurop MTZ80?

    Virtual rep points again I am afraid Glenn.
    Good sound advise all the same!
    Grizzly
    Despite the High Cost of Living it still remains Popular!

  5. #5
    Join Date
    May 2017
    Location
    Sweden
    Posts
    34
    Rep Power
    0

    Re: Oil level on Maneurop MTZ80?

    Thank you Glenn for expert advice! Ok I have to adress this problem as soon as possible then! Last time when I added 0,7 liters I used a bottle with a pointy tip through the oil plug. Will I be able to get more oil in that way or will it come out that same port? Do I need some teflon tape to seal that oil plug? Didn't use anything last time and it did not leak.

  6. #6
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Oil level on Maneurop MTZ80?

    Hi Swedal
    Emkarate oil is ok to use for top up, the additives in the compressors original oil Will have done its job .
    To fill the compressor with oil you can use an oil pump directly in to the 1/4" flare Schroeder fitting. This can be a tiresome job, or an easier way is to fit a system analyser onto the suction valve ,run the compressor into a slight vacuum and dip the charging hose into the oil can. Close the suction valve and the suction inside the shell will suck the oil into the compressor.close the analyser valve once sufficient oil has been added to the compressor, back seat the suction valve and carefully remove the analyser from the compressor. Open the suction valve fully and check the oil level.send me you email on a pm and I'll attach the why comps fail articles for you

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Oil level on Maneurop MTZ80?

    OK.
    Showing my Old Age here!
    What's a System Analyser Glenn?
    Grizzly
    Despite the High Cost of Living it still remains Popular!

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Oil level on Maneurop MTZ80?

    Grizzly my friend.
    Here is a pic of analyzer for you
    40812.jpg

  9. #9
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Oil level on Maneurop MTZ80?

    System analyser used to be called refrigeration technician or engineer!

  10. #10
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Oil level on Maneurop MTZ80?

    Hi Grizz
    Chemi got it right,
    Correct term for a set of gauges = System Analyser
    That what us tech boys call them .
    Ain't this site great we learn something new everyday and for free ,magic ha ha

  11. #11
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Oil level on Maneurop MTZ80?

    I will be retired before we engineers see anything like that!
    Thanks for the update all the same.
    Grizzly
    Despite the High Cost of Living it still remains Popular!

  12. #12
    Join Date
    May 2017
    Location
    Sweden
    Posts
    34
    Rep Power
    0

    Re: Oil level on Maneurop MTZ80?

    Just to make this oil refill clear. I can use both the compressor housings "spare" Schrader valve or the suction valve service port to add oil? I won't damage the compressor by flooding it with oil when it runs? My idea was to isolate compressor and evacuate it. Using vacuum to suck oil into the spare Schrader valve. But if I can do this without evac using the compressor itself that would be great.

  13. #13
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Oil level on Maneurop MTZ80?

    Swedal. Are you a qualified refrigerarion engineer?
    There are a few things in your post that should be clear to every fridgy.
    I an only asking as I'm afraid you might suck air into the compressor and you never heard of hand held oil pump.

  14. #14
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Oil level on Maneurop MTZ80?

    Quote Originally Posted by Grizzly View Post
    I will be retired before we engineers see anything like that!
    Thanks for the update all the same.
    Grizzly
    Dont retire just go fishing more often!

  15. #15
    Join Date
    May 2017
    Location
    Sweden
    Posts
    34
    Rep Power
    0

    Re: Oil level on Maneurop MTZ80?

    Quote Originally Posted by chemi-cool View Post
    Swedal. Are you a qualified refrigerarion engineer?
    There are a few things in your post that should be clear to every fridgy.
    I an only asking as I'm afraid you might suck air into the compressor and you never heard of hand held oil pump.
    Yes I am certified. I usually work on heat pumps and car ac. And yes I know that air does not belong in a refrigeration system. And I have heard of oil pumps but I don't have one because I usually don't need one. I can't find anything contributing in your post though.

  16. #16
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Oil level on Maneurop MTZ80?

    Hej Swedal
    I have used this method several times, as well as the method you were going to do using a vac pump. The vac pump method is simpler but if you haven't a vac pump you use your ingenuity by using the compressor as the vac pump. Ps never do it with a Scroll as you will wreck it.
    Ps The articles will be with you shortly
    Glenn

  17. #17
    Join Date
    Mar 2005
    Location
    u.a.e
    Age
    68
    Posts
    171
    Rep Power
    20

    Re: Oil level on Maneurop MTZ80?

    I would like to add and recommend to have a handy oil pump always in tools kit, It does not cost much and will cover its prices quickly if working on these type of units. Also if a system is working let it pump down to bring back all oil from the system before to charge additional quantity.
    Observed oil problems mostly on the split unit, due to field piping (Long runs, Over sizes, No oil traps or traps at not where it should be) which is not designed and implemented as per recommendations of the manufacturer or industrial codes. Less failures for Package unit as those are perfectly designed and have short piping.
    Compressor should not to use for self vacuum, it is not good for motor winding and may damage it.
    Last edited by malik55; 05-09-2017 at 12:57 AM.

  18. #18
    Join Date
    May 2017
    Location
    Sweden
    Posts
    34
    Rep Power
    0

    Re: Oil level on Maneurop MTZ80?

    Yes I will get myself that oil pump. For this time I used the vacuum method and it worked great. Even got too much oil in it so had to drain some out. Ended up adding 0,6 liters and that seems to work fine. It actually ran just fine without that extra oil for 2 weeks but it should be more safe now.

  19. #19
    Join Date
    Mar 2005
    Location
    u.a.e
    Age
    68
    Posts
    171
    Rep Power
    20

    Re: Oil level on Maneurop MTZ80?

    Mark it the level and keep eye on sight glass, observe it on daily bases if possible for some time, Remove extra oil if sight glass shows above 3/4.
    Let be happy your compressor with proper lubrication.

Posting Permissions