    Carrier chiller 30xa



    I am having Carrier 30xa chilled. One circuit is always tripping by discharge pressure high temperature alarm. Anybody can help me.



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Carrier chiller 30xa

    Hi arulsr47.
    Are you an engineer, a Manager or what?
    What is your role in relation to the errant chiller.
    Please tell us something about your involvement with this chiller and then we can advise accordingly.
    So many first time posts are " I want" requests yours included.
    Some background would be helpful.
    Grizzly
    Despite the High Cost of Living it still remains Popular!

  3. #3
    Join Date
    Aug 2017
    Location
    Sharjah
    Posts
    2
    Rep Power
    0

    Re: Carrier chiller 30xa

    I am a site engineer in a government organisation in dubai. Our team replaced the discharge pressure switch but no use. We cannot able to come to a conclusion like how to rectify the problem. Please advise how to come out from this problem.

  4. #4
    Join Date
    Sep 2010
    Location
    Dorset
    Age
    76
    Posts
    209
    Rep Power
    16

    Re: Carrier chiller 30xa

    Has anybody in your team monitored the pressure during operation?
    Brian, retired in Devon.

  5. #5
    Join Date
    Mar 2005
    Location
    u.a.e
    Age
    68
    Posts
    171
    Rep Power
    20

    Re: Carrier chiller 30xa

    What is chillers model?
    Last edited by malik55; 06-09-2017 at 11:59 PM.

  6. #6
    Join Date
    Mar 2005
    Location
    u.a.e
    Age
    68
    Posts
    171
    Rep Power
    20

    Re: Carrier chiller 30xa

    When you need some advice have to tell the details, No one has such powers that they know the culprit from miles away.
    What is chillers full model number, 30XA is a series?
    What is chillers condenser pressures and temp at that time and which Ref is in the chiller?
    Is chiller works up and then trips or it trips out as start up?
    What is the Alarm code?
    Any machine trips out from H.P there are two reasons, either a real high condenser pressure or a trip out due to controls problem. You have to identify the tripping cause due to what. Check actual condenser pressure and temps at full load by external manifold and thermometer, compare it with the chiller controller and other chillers in the area. Check condenser condition XA chillers comes with special type of condensers, and is not easy to clean as older fins type condensers, Clean it if it is dirty.
    Last edited by malik55; 07-09-2017 at 12:07 AM.

  7. #7
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: Carrier chiller 30xa

    Give full model an serial number is it French or USA made..

  8. #8
    Join Date
    Jan 2011
    Location
    London
    Age
    38
    Posts
    43
    Rep Power
    0

    Re: Carrier chiller 30xa

    Hi Fella
    the carrier 30xa has a actuator fitted on the discharge pipework ive had the same issue and found that the actuator was not opening causing the chiller to trip on high pressure

  9. #9
    Join Date
    Oct 2009
    Location
    Norway
    Posts
    39
    Rep Power
    0

    Re: Carrier chiller 30xa

    Is the high pressure switch manual reset?
    What kind of controller do you have?

    ive had some issues with 30HXC pro dialog plus. It trips on high pressure switch alarm, but the manual high pressure switch didnt trip. It turned out to be a weak link with the compressor board, so it had to be changed or repaired.

  10. #10
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: Carrier chiller 30xa

    XA hp switch is auto reset.

  11. #11
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: Carrier chiller 30xa

    My mistake it's a manual rest on XA auto reset on the RB's