    why water is sweating from grill



    Hi frens..

    Recently, water is sweating from supply Air grill, please any body give me the solution how to control this problem..



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: why water is sweating from grill

    Grill temp is below dew point.
    Evaporating temp is too low or set point is too low.

  3. #3
    Join Date
    Nov 2008
    Location
    nepal
    Posts
    125
    Rep Power
    16

    Re: why water is sweating from grill

    Dear chemi-cool thanks for the information,do you have any suggestion to control it.

  4. #4
    Join Date
    Jan 2012
    Location
    Pakistan
    Age
    43
    Posts
    32
    Rep Power
    0

    Re: why water is sweating from grill

    Dear Anil
    1. you have to put your unit on dehumidification mode or set dehumidification setting lower
    2. Some unit have installed with heaters to control temperature during dehumidification so you can check it also
    3. for immediate solution you can insulate your grill area where water is dropping

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: why water is sweating from grill

    Quote Originally Posted by anil130 View Post
    Dear chemi-cool thanks for the information,do you have any suggestion to control it.
    You never mentioned where the unit is installed and what it is cooling.
    In general, when the grill is below dew point, water from the air will condense on it.
    You have a few options, check the air speed, a filter might be blocked. evaporating temp is too low. Humid air is entering the space.

  6. #6
    Join Date
    Nov 2014
    Location
    Australia
    Age
    31
    Posts
    16
    Rep Power
    0

    Re: why water is sweating from grill

    check for low supply air temp, should be around 12 - 15C ish. low fan speed has been the most common for me, blocked filters, very dirty fan blades or poor commissioning
    also, undersized grilles will do this due to high velocity.

  7. #7
    Join Date
    May 2011
    Location
    India
    Age
    38
    Posts
    106
    Rep Power
    13

    Re: why water is sweating from grill

    Quote Originally Posted by mirza ateeq View Post
    Dear Anil
    2. Some unit have installed with heaters to control temperature during dehumidification so you can check it also
    Can you explain how this heater capacity is arrived at? Q=m(T2-T1)? What will be T2 & T1?

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: why water is sweating from grill

    Check this!

    Condensing on Grilles

    The key issues here are two-fold. Condensation occurs when the temperature of a surface is below the dewpoint of the surrounding air. Therefore, either the dewpoint of the space air is too high or the surface temperature of the grille(s) is/are too low.

    It appears that you may have already found part of the cause in the stuck chill water valve; i.e., the fully open chill water valve is causing reduced supply air temperatures to the point that the grille surface temperature is below the dew point of the air in contact with the grille(s). IF the backs of the gilles are wet, then the attic air is a culprit.

    The suggestions to investigate "leaky attic syndrome" is relevent to the extent that raw outside air that can get into the attic, then heated further so that the air is above the dewpoint of the grille temperature can cause condensation. However, insulating the back of the grilles is not the final solution to the problem. You need to cure the cause of the problem, not the symptom.

    The most common mistake made by service technicians when "sweating" (actually condensation) occurs on the grilles is to close off the outside air feature of the air handler. The opposite is true.

    An auditorium should have a fair amount of outside air to dilute odors and also should conform to ventilation standards per your codes. (ASHRAE recommends 15 cfm per person, as I recall). This can be a HUGE amount of outside air to deal with. If sufficient outside air is introduced to the space, thereby "pressurizing" the auditorium, you will probably solve the problem with the grilles. Even with an open attic ventilator (I recommend that you restrict the size of the ventilator or close it), the outside air that is brought through the cooling coil will be dehumidified AND pressurize the space. If you have little or no "raw" outside air in contact with the grilles, then the drier air should not cause condensation on the front OR the back of the grilles, as the air then passes up to the attic space and out the ventilator penetration in the attic. (assuming the doors are closed to the out of doors).

    Auditoriums are also VERY subject to this sort of problem during startup and especially during part load performance such as a humid 80 degree day. At part load, there can be insufficient coil load to allow for dehumidifying the air effectively, causing high space humidity, thus condensing grilles.

    If the space has been vacant for a few days, upon startup of the system, you probably will have condensation no-matter-what unless you bring the space temperature down slowly, while at the same time bringing in outside air to maintain pressurization of the space.

    The same thing happens in restaurants where there is a LOT of outside air passed thru the space due to the kitchen hood exhaust requirements.

    A worse case scenerio would be to install correctly engineered reheat coils with appropriate controls, but this should only be recommended when all other conventional solutions fail.
    Last edited by nike123; 15-11-2017 at 01:48 PM.