    Submerged copper tube



    Has anyone experience determining the needed copper coil lenght for a given capacity, fed by evoporating refrigerant, submerged in a tank of agitated water that has to cool down to just above freezing temperature of the water?


    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  2. #2
    Join Date
    Mar 2006
    Location
    UK
    Age
    66
    Posts
    92
    Rep Power
    19
    Hi peter
    Rough guess find the evap with the same rate and try and measure the length of pipe. I have worked on many homemade water chillers in my time they all work ok
    if you cant't fix it don't

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Submerged copper tube

    It's not for me, someone asked me.
    Heat load is 8 kW, how many copper pipes has to be submerged in the tank with clean, pumped water?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Jan 2006
    Location
    Adelaide , Australia
    Posts
    192
    Rep Power
    19

    Talking Re: Submerged copper tube

    We have built quite a few chiller tanks with copper coils , the length is important but not critical the longer the better . . The more surface area you have the better, just select the correct orifice for the capacity for the TX valve ( 8KW ) or the correct capillary diameter and length . Flow rate of the water you are cooling over the coil also has an effect .

    This is site has all the technical details http://www.climaticcontrol.com/info/...c_12(rev1).htm


  5. #5
    Join Date
    Jan 2006
    Location
    Adelaide , Australia
    Posts
    192
    Rep Power
    19

    Talking Re: Submerged copper tube

    We have built quite a few chiller tanks with copper coils , the length is important but not critical the longer the better . . The more surface area you have the better, just select the correct orifice for the capacity for the TX valve ( 8KW ) or the correct capillary diameter and length . Flow rate of the water you are cooling over the coil also has an effect .

    This is site has all the technical details
    http://www.climaticcontrol.com/info/...c_12(rev1).htm

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Submerged copper tube

    Well, can you give a rough estimate what you've installed for a certain capacity?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Submerged copper tube

    Well, can you give a rough estimate what you've installed for a certain capacity?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    noddyhead's Avatar
    noddyhead Guest

    Re: Submerged copper tube

    Please find attached, put as much pipe as humanly possible. The more the better is agreed.

    Regards
    Attached Files Attached Files

  9. #9
    Join Date
    Jan 2006
    Location
    Adelaide , Australia
    Posts
    192
    Rep Power
    19

    Re: Submerged copper tube

    Quote Originally Posted by noddyhead
    Please find attached, put as much pipe as humanly possible. The more the better is agreed.

    Regards
    Ah the good old kelvi cheat sheet , you cant go wrong

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Submerged copper tube

    Nodyhead, thanks very, very much. That's exactly what I was looking for.
    And thanks also you took the time to scan this for me.
    If I ever can help you, you know where you can find me.

    Peter
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Submerged copper tube

    Good job Nobby. I was looking for a similar table and couldn't find it. I had a picture of a bundle of tubing from a premix cooler and couldn't find it either. But it is as you say - as much as you can fit!

  12. #12
    Coolers's Avatar
    Coolers Guest

    Re: Submerged copper tube

    When I've designed these type of coils in the past, I've always worked on the following:-

    for 'still' water in a tank, a coil should give :- 20btu/hr per Sq Ft of Surface Area per degree FTD (The TD is the difference between the required finished water temp and the evaporating temp).

    If the water is agitated, this can go up to around :-50 btu/hr per Sq Ft of Surface Area per degree FTD.

    And if you're using 5/8" Copper, this has a surface area of 0.163625 Ft2 Per Foot of tube.

    Always worked for me in the past


    Good luck with it (Oh, and sorry it's in 'old money')

  13. #13
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Submerged copper tube

    Hi Coolers. I haven't looked at the tables to compare your rule of thumb to see how it tracks, but your post had me revisiting thoughts that I had when Peter first posed the question. And that is my observation that the coils I see in post mix agitated water pools are iced up coils - providing near freezing water temperatures as the water forms ice on the coils and recirculates past this insulated barrier of ice.

    So one should assume that ice formation is a necessary part of the load, I suppose? After that, the cooling is done with the latent melting and refreezing of the conditioned water, while the evaporator tubing operates at 10 to 15 degrees below freezing, with a cutout on a low pressure switch?

    I like that term: "old money." I wish there were a way to just type in a number and say "psig" or deg C and have a magic bubble in parentheses show the recalculated number in bars or deg C, or vice versa. What with computers and all. Hint, hint, Dez.

    Anyway, one could not have asked a simpler question than Peter's friend which drives me back into renewed attempts at understanding the basics of what we do and how we do it.

Similar Threads

  1. oxidation scale in copper tube and fittings
    By DeB in forum Fundamentals
    Replies: 8
    Last Post: 23-06-2006, 09:45 PM
  2. metric capillary tube
    By tralex in forum Fundamentals
    Replies: 5
    Last Post: 21-02-2006, 06:57 AM
  3. The amazing Mr. Cap Tube
    By shogun7 in forum Domestic
    Replies: 52
    Last Post: 07-01-2006, 07:33 PM
  4. reduce thickness of bended copper tubes
    By rlim in forum Air Conditioning
    Replies: 4
    Last Post: 08-07-2003, 10:58 PM
  5. Tube staggered/squared
    By bersaga in forum Fundamentals
    Replies: 2
    Last Post: 05-01-2003, 11:56 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •