    Mitsubishi Heavy Industries



    Model FDCA450HKXRE4A
    I'm getting a compressor start up fault on 1 of 2 compressors. Getting no voltage to the compressor although contactor pulls in. I've replaced the inverter pcb but still the same
    Any suggestions please??



  2. #2
    Join Date
    Feb 2011
    Location
    England
    Posts
    22
    Rep Power
    0

    Re: Mitsubishi Heavy Industries

    Have you checked voltage at the contactor? We need more info?

  3. #3
    Join Date
    Feb 2009
    Location
    telford
    Posts
    1,849
    Rep Power
    24

    Re: Mitsubishi Heavy Industries

    Sounds like a breaker in the control panel has tripped check the power to the contactor is this single or three phase?