Results 1 to 8 of 8
    Jul 2017
    8
    Mitsubishi Heavy Industries
    Model FDCA450HKXRE4A
    I'm getting a compressor start up fault on 1 of 2 compressors. Getting no voltage to the compressor although contactor pulls in. I've replaced the inverter pcb but still the same
    Any suggestions please??
    Feb 2011
    31
    Re: Mitsubishi Heavy Industries
    Have you checked voltage at the contactor? We need more info?
    Feb 2009
    telford
    2,068
    27
    Sounds like a breaker in the control panel has tripped check the power to the contactor is this single or three phase?
    Jul 2017
    8
    Yes I have three phases across both sides of the contactor.
    Mar 2005
    u.a.e
    166
    14
    One of the Compressor is not working, which one, 1 or 2- What is the fault code?
    If you have voltage across Contactor then it means it is energized (or stuck permanently which you can check by turning power off, if still in then it is defective), Otherwise it is normal, all the safeties are satisfied and control is okay, then the fault is in the power module.
    You said that you have replaced the Inverter board, Is it a new one or removed from some ware, Are you sure that the board is okay, Also you have to check two other components mentioned as DM and PWB (which is a noise filter), I have not seen this unit and only refer from the drawing.
    It should be noted that you have to take extreme care wile working on electrical controls especially inverter type
    units, as there are capacitors in the circuit and have charge even power is switched off.
    Try to get controls manual and check accordingly.
    Jul 2017
    8
    Thanks Malik55. The fault code I am getting is E59. It's the no1 compressor. Yes it is a new inverter board.
    Mar 2005
    u.a.e
    166
    14
    Try to get service manual from the dealer, It is always good practice to follow what the manufacture said.
    Looks it is old model as service manual is not available by search,
    Compare both compressors winding readings, earth M-Ohms, Condenser fan motors and electrical power boards.
    If condenser fan FM01 1 has some problem may possible system will not come on. Also there are other Boards such as DM-1 (Diode Module), PWB (Noise filter), IPM(Intelligent power module) needs to be checked.
    Jul 2017
    8
    Ok. Thank you ��