25-05-2006, 12:41 AM #1
Daikin VRV
I've just joined the site and I'd like to say hello to everyone. I've got an intermittent EO fault with a Daikin RSEY10GJV1. I've checked all the usual suspects but so far have drawn a blank. I spoke to a guy at Daikin UK today who suggested fitting some ''tell tales'' accross all the compressor overheats and fan klixons etc. Apparently they blow when the switch they are connected to opens making it easier to pinpoint the fault. Has any one heard of these devices, and do you know what they are called and where they are available from? I'd be gratefull for any feedback.
Regards, Nick.
-
25-05-2006, 07:42 AM #2
Re: Daikin VRV
Tell tales? They blow... they "who"?
-
25-05-2006, 03:01 PM #3
Re: Daikin VRV
Can't the guy at Daikin tell you
-
25-05-2006, 06:11 PM #4
Re: Daikin VRV
Originally Posted by nickthefridge
The EO fault is a protection device for the outdoor unit. Check for continuity on the GREY wires coming off the PCB. These go through the internal "overloads" of the fan motor and compressor. The PCB gives out 240v and expects it back but in a fault condition the circuit becomes open circuit hence the fault code.
With the EO code showing don't do anything until you've checked for continuity otherwise you will reset the system and the fault will disappear - until next time
-
25-05-2006, 07:34 PM #5
Re: Daikin VRV
Originally Posted by frankTakes a licking, keeps on ticking.
-
25-05-2006, 07:46 PM #6
Re: Daikin VRV
Hi Guys,
Check out the Thread Daikin VRV's from 14-01-2006 in the air conditioning forum.
Have come accross they tell-tales before and they are useful for iscolating faults.
i assume they are available from Daikin although Frank will know better than i do
Regards
-
26-05-2006, 06:55 PM #7
Re: Daikin VRV
Never had to use the tell tales and i know that they are not available from Daikin. I would recommend power off the system and switching to emergency which will run the standard compressor alone without the inverter allowing you to check the running current 95% of the time its either standard compressor overload or HP trip. Once you get the system running on emergency check that the valves are not passing through the inverter compressor allowing discharge gas back into the suction! If so your inverter compressor is dud! Hope this helps
-
26-05-2006, 09:48 PM #8
Re: Daikin VRV
Originally Posted by puddleboy3
EO should be fairly easy to check as if it's an overheat problem -comp fan etc then it will need some time to reset but a hp fault will clear rapidly. plus your gauges would tell you quickly. Now an intermittent EO is another fish
Cheers
Richard
Cheers
Richard
-
26-05-2006, 11:12 PM #9
Re: Daikin VRV
Originally Posted by rbartlettLast edited by puddleboy3; 26-05-2006 at 11:15 PM.
-
14-10-2007, 01:17 PM #10
-
14-10-2007, 01:42 PM #11
Re: Daikin VRV
Isnt this just a clasic undercharge problem, overheating the compressor after prelonged use and resetting by the time the engineer arrives on site, Id stick abit of gas in and monitor for afew days, If problem goes away I would decant , pressure test and recharge with correct weight of gas. Or decant pressure test and recharge first off depends on what sort of contract you have.
Similar Threads
-
Daikin Refnet Position
By puddleboy3 in forum Air ConditioningReplies: 15Last Post: 13-02-2009, 04:12 PM -
Daikin Analyzer
By marc5180 in forum FundamentalsReplies: 10Last Post: 02-08-2008, 07:15 PM -
Daikin Controllers
By airefresco in forum Air ConditioningReplies: 5Last Post: 15-05-2008, 08:08 AM -
!!big Daikin Problem!! Codes,u4,pj, And E0
By airconengineer in forum Air ConditioningReplies: 21Last Post: 31-05-2007, 09:04 PM -
Daikin KRP2A61 Card Power consumption
By EddieC in forum Air ConditioningReplies: 5Last Post: 19-08-2006, 04:08 PM