    Pressure drop at condenser



    Hi friends,

    At Evapco documents regarding condensers I read that when a condenser works it has pressure drop during pipes and while it is idle , It has not any pressure drop and pressure of inlet would be same with pressure of outlet.

    Would it be possible someone make it clear for me, Why when condenser does not work it has not pressure drop ?

    Please see photo at below

    44.jpg



  2. #2
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    439
    Rep Power
    31

    Re: Pressure drop at condenser

    Friction pressure losses and changes in saturation temperature in the dynamic system (operating condenser)
    I love the smell of Ammonia in the morning!

  3. #3
    Join Date
    Sep 2010
    Location
    Dorset
    Age
    76
    Posts
    209
    Rep Power
    16

    Re: Pressure drop at condenser

    Pressure drop is due to friction losses along the pipe length when the fluid is moving along the pipe.

    When the flow stops the friction loss also stops leaving just the static pressure which is equal throughout the system.
    Brian, retired in Devon.

  4. #4
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Pressure drop at condenser

    We have pressure drop when someting (vapour, liquid) moving inside the pipe. Nothing is moving inside of idle condenser.