Results 1 to 3 of 3
  1. #1
    Join Date
    Nov 2008
    Location
    us
    Age
    60
    Posts
    67
    Rep Power
    16

    York millennium ycch163 rotary screw compressor



    I understand the slide valve operation, but I do have a question about when the system is down. On this particular chiller there is no external oil pump to drive the slide back to minimal position for start-up. I can only assume (which I hate to do) that there is an internal spring that forces the slide back to minimal position, or ?? Thanks.



  2. #2
    Join Date
    Jul 2007
    Location
    Czech
    Age
    61
    Posts
    374
    Rep Power
    18

    Re: York millennium ycch163 rotary screw compressor

    Yes, the spring is forcing unloading.
    Josef.

  3. #3
    Join Date
    Feb 2006
    Location
    Hampshire
    Posts
    61
    Rep Power
    19

    Re: York millennium ycch163 rotary screw compressor

    What's the compressor? Is it the dxs?

    If you're having load / unload issues, it's not unknown for the springs to break on these and require replacement.