Results 1 to 4 of 4
  1. #1
    Join Date
    Mar 2007
    Location
    Egypt
    Age
    49
    Posts
    40
    Rep Power
    0
    high superheat forsab 28 cmo
    Hello Friends
    i have sab comp. type cmo28 work with R22 when it run full gives high super heat 135C
    it has not oil cooler or TEX for injection liquid . is that normal ?
  2. #2
    Join Date
    Sep 2010
    Location
    Dorset
    Age
    69
    Posts
    209
    Rep Power
    10
    Re: high superheat forsab 28 cmo
    Possibly not, read the expected temperatures here...
    Page 57, 58
    http://bit.ly/2uOtFTF
    Brian, retired in Devon.
  3. #3
    Join Date
    Mar 2007
    Location
    Egypt
    Age
    49
    Posts
    40
    Rep Power
    0
    Quote Originally Posted by FaultCode View Post
    Page 57, 58
    Thank you for your advice
  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    2,506
    Rep Power
    27
    It's (almost) impossible to get 135 C superheat under normal circumstances.
    Check suction temperature sensor & its connections.
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts