    Check valve for discharge pipe



    Dear All,

    I heard that when air-cooled condenser is above of compressor, We must use check valve at discharge pipe of compressor.
    Why we should check valve ? for prevent returning liquid on top of valve plate of compressor ? Or it has other reason ?
    If we use "Inverted P trap" at inlet of condenser, It is not enough for prevent liquid migration ?

    Thanks if you help me in this topic.

    With best regards.



  2. #2
    Join Date
    Sep 2010
    Location
    Dorset
    Age
    76
    Posts
    209
    Rep Power
    16

    Re: Check valve for discharge pipe

    Yes a check valve or inverted trap should be fitted at the condenser inlet.

    This McQuay design guide might be of help to you, see page 15. http://bit.ly/2w4dsHI
    Last edited by FaultCode; 27-07-2017 at 07:55 PM. Reason: Wrong page number
    Brian, retired in Devon.

  3. #3
    Join Date
    Jul 2017
    Location
    Qatar
    Age
    43
    Posts
    34
    Rep Power
    0

    Re: Check valve for discharge pipe

    Quote Originally Posted by FaultCode View Post
    Yes a check valve or inverted trap should be fitted at the condenser inlet.

    This McQuay design guide might be of help to you, see page 15. http://bit.ly/2w4dsHI

    Thanks a lot

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Check valve for discharge pipe

    Refrigerant migrates to the cold place and to the lower place.
    Check valve before the condenser will stop the liquid in the condenser from migrating to the compressor discharge chamber and rist the discharge valves from braking at start up.

  5. #5
    Join Date
    Mar 2016
    Location
    IRAN
    Posts
    182
    Rep Power
    9

    Re: Check valve for discharge pipe

    Quote Originally Posted by GENERALCOOL View Post
    Dear All,

    I heard that when air-cooled condenser is above of compressor, We must use check valve at discharge pipe of compressor.
    Why we should check valve ? for prevent returning liquid on top of valve plate of compressor ? Or it has other reason ?
    If we use "Inverted P trap" at inlet of condenser, It is not enough for prevent liquid migration ?

    Thanks if you help me in this topic.

    With best regards.


    This photo is your answer
    1.jpg

  6. #6
    Join Date
    Sep 2016
    Location
    Ecuador
    Age
    52
    Posts
    6
    Rep Power
    0

    Re: Check valve for discharge pipe

    Hi all,
    Recently we discovered some issues with check valves mounted in the discharge line of a multiple R507 compressor system (6 VSD controlled DMW piston). After an issue in the oil separator we found some inner parts of the valves back in the bottom of the separator and it showed several failed.
    How your dealing normal with preventive maintenance on these types, as it's a bit difficult when they are soldered in the discharge lines

    Thanks your thoughts guys

    NRVH Check.jpg
    NRVH.jpg

  7. #7
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Check valve for discharge pipe

    There is no preventative maintenance for these non return valves apart from selecting the correct valves for the system design.
    Check valves for use with variable speed drives are difficult to select as the gas volume can vary by a large amount.
    When selecting NRV's it is selected against the volume flow that will keep the valve fully open. If the valve is not kept fully open because the volume flow is too low then the piston starts to chatter and bang open and closed causing it to break.
    The NRVH has a heavier return spring and will cause the piston to bang up and down until destruction occurs.
    A better solution would be the NRV with the lighter spring as it needs less flow to lkeep it open. With discharge gas flows frequencies and harmonics can be a disastrous situation .
    With piston compressors if the nrv is not sized correctly the nrv piston will oscillate at the same rate as every piston pulsation say an 8 cylinder compressor running at 1500 rpm running for 1 hour will lead to the nrv piston oscillating 720,000 times an hour . At that rate it won't last for very long, also the Ptfe seat will be smashed to pieces,preventing it from closing tight.
    An Nrv should be a smaller size than its surrounding pipe work so that it creates a small pressure drop helping to keep it in the fully open position and allowing the NRV to safely to its job

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Check valve for discharge pipe

    Excellent advice Glenn.
    Thanks Grizzly
    Despite the High Cost of Living it still remains Popular!

  9. #9
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Check valve for discharge pipe

    Quote Originally Posted by A.Mortezania View Post
    This photo is your answer
    1.jpg
    I know this photo is from AC_Guide_McQuay, but for me a very bad example of refrigerant piping .... in this case discharge line from compressor/s to condenser/s ...

    Discharge pipe should run straight vertical above condenser (without horizontal runs - if possible) and then down to condenser inlet (in this case - two elbows less) and without inverted trap. Just at highest point of discharge pipe (this should be above condenser) we can install NRV-check valve and after that pipe must run with slope to condenser inlet.

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.